Hi all guy
To day I'm tested automatic shutdown with our system, but look seen shutdown process not correctly,
My environment is, vSphere 6.5 (VC and ESXi) we have physical server was installed PCNS 4.2.
Due testing Host (esxi02) can't shutdown by PCNS, please kindly help to investigate the problem.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:16 AM . Last Modified: 2024-03-12 11:49 PM
Hi,
I see a few issue in the error log
07-02-17 12:42:55,934 ERROR Thread-51 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - getESXiHostConnection, Host 192.168.14.12 - (NoPermission or InvalidLogin) [no details available]
07-02-17 12:42:55,934 ERROR Thread-51 com.apcc.m11.components.Shutdowner.Hosts.ESXManagedHost - checkForVCSAVMAndHostInCriticalHosts - cannot obtain HostSystem using findByIP and findByDnsName for critical host 192.168.14.12
07-02-17 12:43:16,370 ERROR pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - Unable to connect to vCenter Host 192.168.14.14 - java.rmi.RemoteException: VI SDK invoke exception:java.net.ConnectException: Connection refused: connect
07-02-17 12:43:17,400 ERROR pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - getVCenterServerConnection, Host 192.168.14.14 - . VI SDK invoke exception:java.net.ConnectException: Connection refused: connect
07-02-17 12:45:02,841 ERROR Thread-51 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - Unable to log directly into host (NoPermission or InvalidLogin): 192.168.14.12
Have you created a local account that PCNS can use to access the host? See the trouble shooting section of the PCNS 4.2 VMware User's Guide (page 137 and 138).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:16 AM . Last Modified: 2024-03-12 11:49 PM
Hi,
I see a few issue in the error log
07-02-17 12:42:55,934 ERROR Thread-51 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - getESXiHostConnection, Host 192.168.14.12 - (NoPermission or InvalidLogin) [no details available]
07-02-17 12:42:55,934 ERROR Thread-51 com.apcc.m11.components.Shutdowner.Hosts.ESXManagedHost - checkForVCSAVMAndHostInCriticalHosts - cannot obtain HostSystem using findByIP and findByDnsName for critical host 192.168.14.12
07-02-17 12:43:16,370 ERROR pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - Unable to connect to vCenter Host 192.168.14.14 - java.rmi.RemoteException: VI SDK invoke exception:java.net.ConnectException: Connection refused: connect
07-02-17 12:43:17,400 ERROR pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - getVCenterServerConnection, Host 192.168.14.14 - . VI SDK invoke exception:java.net.ConnectException: Connection refused: connect
07-02-17 12:45:02,841 ERROR Thread-51 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - Unable to log directly into host (NoPermission or InvalidLogin): 192.168.14.12
Have you created a local account that PCNS can use to access the host? See the trouble shooting section of the PCNS 4.2 VMware User's Guide (page 137 and 138).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:16 AM . Last Modified: 2024-03-12 11:48 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:16 AM . Last Modified: 2024-03-12 11:48 PM
After create shard user on vCenter and ESXi host, automatic shutdown working normally
Thank you. 🙂