Hi All,
I just installed an AP9630 into and SUA2200xl. The card seemed to work fine after installation and I was able to see my UPS unit and logs. I updated the firmware to 5.1.7 for some of the new email configurations and I can no longer see the UPS tab or any UPS log information.
Any ideas?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:30 AM . Last Modified: 2024-03-11 01:19 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:30 AM . Last Modified: 2024-03-11 01:19 AM
Thank you kindly!
That was indeed the case. I did not think to check more than the management card type.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:29 AM . Last Modified: 2024-03-11 01:19 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:29 AM . Last Modified: 2024-03-11 01:19 AM
All three components listed below
Application Module:
Name: sy
Version: v5.1.7
Date: Dec 1 2011
Time: 13:10:10
APC OS (AOS):
Name: aos
Version: v5.1.7
Date: Nov 22 2011
Time: 09:53:57
APC Boot Monitor:
Name: bootmon
Version: v1.0.2
Date: Jan 21 2010
Time: 13:35:57
null
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:30 AM . Last Modified: 2024-03-11 01:19 AM
If you click on administration, then general, then about, What is the name for the firmware? One should be AOS, the other should be SUMX or SY, SY3P etc.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:30 AM . Last Modified: 2024-03-11 01:19 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:30 AM . Last Modified: 2024-03-11 01:19 AM
Thank you kindly!
That was indeed the case. I did not think to check more than the management card type.
Link copied. Please paste this link to share this article on your social media post.