Smartups 1000I caused computer to hard shut down & need help to diagnose.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smartups 1000I caused computer to hard shut down & need help to diagnose.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:29 AM . Last Modified: ‎2024-03-11 01:19 AM

0 Likes
3
909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:29 AM . Last Modified: ‎2024-03-11 01:19 AM

Smartups 1000I caused computer to hard shut down & need help to diagnose.

Hi,
I have a Smartups SUA 1000I, (240v) purchased march 2004. I have a Mac and CRT Monitor, PC and CRT Monitor, 2 Synthesizers and a sound card hooked up, with one spare input. These in total are well within the recommended power draw. In fact only 3 LEDs are lit on the Load side. The batteries were changed almost 3 years ago.

Just to note: Ive never used Powerchute because:
- I run a Mac and a PC off my UPS and the PC isnt on for long periods of time.
- Generally my rule is ... If either machine sits idle for more than 2hours I turn it/them off OR if Im out of earshot range of ups alarm for more than 10 mins I'll turn computer/s off.

So, yesterday I was on PC and suddenly everything just stopped dead doing a hard shut down. No warning beeps, nothing from UPS. I cant say for sure how many LEDS were lit on the right side prior but looked down after dropping its load and Online was lit and one green LED on right hand side. Knowing something weird was up I didnt wait around. I unplugged everything in the following order which I have always done.

I turned off UPs pushing its button > switched off power at the wall > unplugged battery connector. UPS was barely even warm around vents. Ambient temp around 22Degr Cent. I didnt know usual reset buttons position (how far out it protruded) so just pushed it and it just came out to the same as it was before I pushed it. (just slightly under 1/4 inch)

I Went to reseat Batt Connector and my husband said he saw all lights at the front flash on and off very quickly, plus there was an extremely fast beeping. Quickly unplugged the Batt Conn again. Waited 2 minutes and tried it again. This time there was a red light on. No alarm. Power was not switched on at wall yet nor had I pushed the power on button.

Husband tested batteries with a fairly new multimeter (about 6 months old) and they were 13.2volts each, so I take it that is normal???.

We tried powering up again and then we got the replace battery/battery disconnected light, flashing with the beeps every few seconds. Not sure exactly how long between beeps or how long it flashed for but it was between 1 or 2 mins. Decided to unplug everything again and when we unplugged the Batt Conn all the lights on the front did the same as B4 plus the very fast alarm.

2 main QUESTIONS are ....Could it be that the Batt Conn plug at the back has become worn and if so is it fixable? and have I been wrong in disconnecting this part of the UPS as an extra measure against premature battery wear.? I say this becasue at certain times, like, if the power is being unstable after a large powercut, we've tended to fully close down the UPS including pulling the Batt Conn .... especially if theres power issues at night, or we're going out and the weather looks stormy. We live rurally and so get more power issues.

Any help much appreciated
Musical

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery_connector_plug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:29 AM . Last Modified: ‎2024-03-11 01:19 AM

0 Likes
0
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:29 AM . Last Modified: ‎2024-03-11 01:19 AM

Hi,
I have a Smartups SUA 1000I, (240v) purchased march 2004. I have a Mac and CRT Monitor, PC and CRT Monitor, 2 Synthesizers and a sound card hooked up, with one spare input. These in total are well within the recommended power draw. In fact only 3 LEDs are lit on the Load side. The batteries were changed almost 3 years ago.

Just to note: Ive never used Powerchute because:
- I run a Mac and a PC off my UPS and the PC isnt on for long periods of time.
- Generally my rule is ... If either machine sits idle for more than 2hours I turn it/them off OR if Im out of earshot range of ups alarm for more than 10 mins I'll turn computer/s off.

So, yesterday I was on PC and suddenly everything just stopped dead doing a hard shut down. No warning beeps, nothing from UPS. I cant say for sure how many LEDS were lit on the right side prior but looked down after dropping its load and Online was lit and one green LED on right hand side. Knowing something weird was up I didnt wait around. I unplugged everything in the following order which I have always done.

I turned off UPs pushing its button > switched off power at the wall > unplugged battery connector. UPS was barely even warm around vents. Ambient temp around 22Degr Cent. I didnt know usual reset buttons position (how far out it protruded) so just pushed it and it just came out to the same as it was before I pushed it. (just slightly under 1/4 inch)

I Went to reseat Batt Connector and my husband said he saw all lights at the front flash on and off very quickly, plus there was an extremely fast beeping. Quickly unplugged the Batt Conn again. Waited 2 minutes and tried it again. This time there was a red light on. No alarm. Power was not switched on at wall yet nor had I pushed the power on button.

Husband tested batteries with a fairly new multimeter (about 6 months old) and they were 13.2volts each, so I take it that is normal???.

We tried powering up again and then we got the replace battery/battery disconnected light, flashing with the beeps every few seconds. Not sure exactly how long between beeps or how long it flashed for but it was between 1 or 2 mins. Decided to unplug everything again and when we unplugged the Batt Conn all the lights on the front did the same as B4 plus the very fast alarm.

2 main QUESTIONS are ....Could it be that the Batt Conn plug at the back has become worn and if so is it fixable? and have I been wrong in disconnecting this part of the UPS as an extra measure against premature battery wear.? I say this becasue at certain times, like, if the power is being unstable after a large powercut, we've tended to fully close down the UPS including pulling the Batt Conn .... especially if theres power issues at night, or we're going out and the weather looks stormy. We live rurally and so get more power issues.

Any help much appreciated
Musical

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:29 AM . Last Modified: ‎2024-03-11 01:19 AM

0 Likes
0
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:29 AM . Last Modified: ‎2024-03-11 01:19 AM

Ok so my husband just tried the light and the front battery lit up the little bulb and the back one there was nothing.

So should I try and see if it will charge the battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:29 AM . Last Modified: ‎2024-03-11 01:19 AM

0 Likes
0
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:29 AM . Last Modified: ‎2024-03-11 01:19 AM

Thanks Wwallender for your response.

Sorry I need a bit more of an explanation. I described 2 scenarios in respect to beeps and lights, neither of which, as I understand it, are normal because....

1/ The troubleshooter in the manual says "All leds are lit and the UPS emits a Constant Beeping - Problem and possible cause : Internal UPS fault - Do not attempt to use the UPS. Turn the UPS off and have it serviced immediately" and
2/ Going by the ( APC) excerpt below, Id also have to conclude something isnt normal here because I got no warnings whatsoever about a low battery, and an UPS shouldnt just dump its load.

QUOTE:
How do I troubleshoot the Replace Battery LED on a Smart-UPS?
Published 09/03/2008 10:59 PM | Updated 01/01/2010 04:58 PM | Answer ID 9383
The replace battery light on my Smart-UPS is on, what do I do?
The Replace Battery LED is designed to illuminate one to two months before the battery actually has to be replaced.
UNQUOTE

No I dont know how to put a 12v load on, or understand about the amperage side to it. Could you please explain about that. My husband said he'll try the light thing tonight, but hes not sure either about the amperage.

Also what do you mean by the capacitors discharging?

I know somethings wrong but I'd like to diagnose exactly what it is if possible so I know if its fixable.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:29 AM . Last Modified: ‎2024-03-11 01:19 AM

0 Likes
0
912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:29 AM . Last Modified: ‎2024-03-11 01:19 AM

Hi,
I have a Smartups SUA 1000I, (240v) purchased march 2004. I have a Mac and CRT Monitor, PC and CRT Monitor, 2 Synthesizers and a sound card hooked up, with one spare input. These in total are well within the recommended power draw. In fact only 3 LEDs are lit on the Load side. The batteries were changed almost 3 years ago.

Just to note: Ive never used Powerchute because:
- I run a Mac and a PC off my UPS and the PC isnt on for long periods of time.
- Generally my rule is ... If either machine sits idle for more than 2hours I turn it/them off OR if Im out of earshot range of ups alarm for more than 10 mins I'll turn computer/s off.

So, yesterday I was on PC and suddenly everything just stopped dead doing a hard shut down. No warning beeps, nothing from UPS. I cant say for sure how many LEDS were lit on the right side prior but looked down after dropping its load and Online was lit and one green LED on right hand side. Knowing something weird was up I didnt wait around. I unplugged everything in the following order which I have always done.

I turned off UPs pushing its button > switched off power at the wall > unplugged battery connector. UPS was barely even warm around vents. Ambient temp around 22Degr Cent. I didnt know usual reset buttons position (how far out it protruded) so just pushed it and it just came out to the same as it was before I pushed it. (just slightly under 1/4 inch)

I Went to reseat Batt Connector and my husband said he saw all lights at the front flash on and off very quickly, plus there was an extremely fast beeping. Quickly unplugged the Batt Conn again. Waited 2 minutes and tried it again. This time there was a red light on. No alarm. Power was not switched on at wall yet nor had I pushed the power on button.

Husband tested batteries with a fairly new multimeter (about 6 months old) and they were 13.2volts each, so I take it that is normal???.

We tried powering up again and then we got the replace battery/battery disconnected light, flashing with the beeps every few seconds. Not sure exactly how long between beeps or how long it flashed for but it was between 1 or 2 mins. Decided to unplug everything again and when we unplugged the Batt Conn all the lights on the front did the same as B4 plus the very fast alarm.

2 main QUESTIONS are ....Could it be that the Batt Conn plug at the back has become worn and if so is it fixable? and have I been wrong in disconnecting this part of the UPS as an extra measure against premature battery wear.? I say this becasue at certain times, like, if the power is being unstable after a large powercut, we've tended to fully close down the UPS including pulling the Batt Conn .... especially if theres power issues at night, or we're going out and the weather looks stormy. We live rurally and so get more power issues.

Any help much appreciated
Musical

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore