AP9619 - Smart-UPS RT 20000 XL: No able to get OIDs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9619 - Smart-UPS RT 20000 XL: No able to get OIDs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
3
1802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

AP9619 - Smart-UPS RT 20000 XL: No able to get OIDs

Hello,

I'm moniroting my APC RT 20k with Zabbix, but I'm unable to get all the OIDs in order to create new alerts for each individual events as I saw in the webpage and I'm listing below:

Event Actions for Individual Events
 
To list all events in a main category by severity level, click the main category name. To list all events in a sub-category by severity level, click the sub-category name.
 
Power Events Environment Events System Events
Input Line Status Communication Mass Configuration
Output Line Status Temperature Security
Battery Humidity  
Bypass I/O Contact  
Communication Relays  
Device    
Diagnostics    
Temperature    
Scheduling

The command I running is snmpwalk -Os -c public -v 1 10.80.18.200 and snmpwalk -Os -c public -v 2c 10.80.18.200 but the information I got from these is not enough.

Could you please help me to solve this incovenience?

Thank you,

Pablo

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 20000
  • ap9619
  • oid
  • oids
  • smart
  • snmpwalk
  • ups
  • zabbix
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
1802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

Hi Pablo,

Do you have the APC MIB loaded? It is available from here -> http://www.apc.com/tools/download/index.cfm Also, any of the APC SNMP OIDs would start with .1.3.6.1.4.1.318 as 318 is the enterprise in the MIB. This is .iso.org.dod.internet.private.enterprises.apc.  You may need to specify where to start your walk I think and find the correct syntax, after you ensure you have the PowerNet MIB from APC compiled and loaded. 

Previous customers I've dealt with using snmpwalk have told me that they thought snmpwalk would poll the device for *ALL* possible OIDs a device provides and that the MIB file would help to map the friendly names to those OIDs but apparently snmpwalk also relies on some other definition (MIB or otherwise) of which specific OIDs to poll. I am not too familiar with it though and have only heard of its existance. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:03 PM

0 Likes
0
1802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:03 PM

Angela,

Thank you.

I accesed to the PowerNet MIB script but I don't know how to install it, could you please provide me the steps?

ftp://ftp.apc.com/apc/public/software/pnetmib/mib/414/powernet414.mib

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
1803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

Hi Pablo,

Do you have the APC MIB loaded? It is available from here -> http://www.apc.com/tools/download/index.cfm Also, any of the APC SNMP OIDs would start with .1.3.6.1.4.1.318 as 318 is the enterprise in the MIB. This is .iso.org.dod.internet.private.enterprises.apc.  You may need to specify where to start your walk I think and find the correct syntax, after you ensure you have the PowerNet MIB from APC compiled and loaded. 

Previous customers I've dealt with using snmpwalk have told me that they thought snmpwalk would poll the device for *ALL* possible OIDs a device provides and that the MIB file would help to map the friendly names to those OIDs but apparently snmpwalk also relies on some other definition (MIB or otherwise) of which specific OIDs to poll. I am not too familiar with it though and have only heard of its existance. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:03 PM

0 Likes
0
1803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:03 PM

Angela,

Thank you.

I accesed to the PowerNet MIB script but I don't know how to install it, could you please provide me the steps?

ftp://ftp.apc.com/apc/public/software/pnetmib/mib/414/powernet414.mib

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:45 AM . Last Modified: ‎2024-02-29 11:03 PM

0 Likes
0
1802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:45 AM . Last Modified: ‎2024-02-29 11:03 PM

Yup, snmpwalk will "fall off the end" of the SNMPv2-SMI::mib-2 tree. To get the vendor-specific information, you have to specify a starting OID on the snmpwalk command line. The user probably wants something like snmpwalk -c public -v 2c 10.80.18.200 1.3.6.1.4.1.318

On a Smart-UPS 1000 I have here, that returns 585 lines. The PowerNet MIB file is important if you have a monitoring system that can import it and display the actual OID descriptions, but for snmpwalk or other tools (such as MRTG), you can just specify the OID by number and not deal with importing the MIB file. Most of the OIDs of interest can be found with web searches like "APC runtime OID".

Unfortunately, the method for importing a MIB into a monitoring system is different for each of those systems, so you'll need to refer to the documentation for your monitoring system to determine how to import it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore