Issues on ATS 7724

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Issues on ATS 7724
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
3
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

Issues on ATS 7724

Hello,

i got following issue:

I connect my two Inputs A & B to the device -> Okey

When i disconnect Input B the ATS switches to A -> Okey

When i reconnect Input B the ATS shows that B is available again -> Okey

But:

When i disconnect Input A the Output goes Off. So Switching is normal when on Input A got a working Power Source. If this Source is available i can switch between those two sources. But if Source A is not available no switching is possible and the ATS doesn't switch to Input B.

I flashed newest firmware and from this point of view the ATS is working, but the main use case is not. So any ideas or questions?

Thanks,

Michael

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

Hi Angela,

yes the output LED goes off and source B input is green.

When ATS of off source B everything is fine. If i have a source A and B connected and i am choosing source B it's okey, too. But if source A goes off, the ATS powers down the output, although source B is on.

I also tested what you said. I swaped the sources but it is exactly same behaviour. So will open a RMA case with our supplier.

 

Greets,

Michael

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

Hi Michael,

Could you please share the following information for us to help further?

  • event.txt, data.txt, and config.ini log files (Instructions to download are here if you need them -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 )
  • Screenshot of Event Counts screen from web or serial/telnet/ssh screen
  • Details on Source A and B - are they UPSs, utility power, generator, etc
  • The first six digits/characters of the ATS serial number
  • How long has the ATS been in service?

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

Hi Michael,

Does the output LED go off on the front too when you said the actual output/load loses power?

If you power the ATS only off of source B, does everything work? It sounds like it based on what I see in the data log - the ATS at least shows it is running off of B.

But, if it won't switch, the only thing I'd be concerned about if it is seeing B as "bad" for some reason but that can be quickly ruled out if A and B are the same circuit or if you swap the sources and plug B into Source A as a test.

There very well could be an issue with a relay somewhere or something. You may want to contact your local support to open a case and pursue a replacement under warranty.

Also, I just wanted to share that we don't really recommend connecting an ATS directly to a generator or utility power and if you do, keep the settings as you have them now with lower sensitivity, wide transfer range, etc. You can also consider changing the preferred source to "none" to prevent some unneed switching.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

0 Likes
0
897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:44 AM . Last Modified: ‎2024-02-29 11:04 PM

Hi Angela,

yes the output LED goes off and source B input is green.

When ATS of off source B everything is fine. If i have a source A and B connected and i am choosing source B it's okey, too. But if source A goes off, the ATS powers down the output, although source B is on.

I also tested what you said. I swaped the sources but it is exactly same behaviour. So will open a RMA case with our supplier.

 

Greets,

Michael

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of