Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

AP9619, AP9618, AP9617 Firmware Question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: AP9619, AP9618, AP9617 Firmware Question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
ryan.schwellenbach_apc
Ensign ryan.schwellenbach_apc
Ensign

Posted: ‎2021-07-08 12:46 AM

0 Likes
2
1586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:46 AM

AP9619, AP9618, AP9617 Firmware Question

This was originally posted on APC forums on 6/23/2015


Hello,

We would like to bring all of our GEN1 NICs up to date on firmware and have a few questions:

  1. What is the most recent version? Also, are the cards AP9619, AP9618, AP9617 all compatible with the same firmware versions?
  2. Is there a utility that can be used to push the firmware to a large number of devices, similar to the GEN2 utility used to upgrae to AP9631 cards to v6.2.0?
  3. Are there any known issues when upgrading the firmware on GEN1 cards? We will be upgrading remotely and would not have physical access to a card if it failed. 

Thanks!

Ryan

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9617
  • ap9618
  • ap9619
  • firmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:46 AM

0 Likes
0
1584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:46 AM

This reply was originally posted by Angela on APC forums on 6/23/2015


Hi Ryan,

1.) It depends on the UPS/device it goes in. Let's assume Smart-UPS - it would be AOS 3.7.3/sumx application v3.7.2. Look for part number SFSUMX372 on the firmware download page. AP9617/18/19 would always use the same firmware. I can't think of a time that they wouldn't when used in a UPS.

2.) Yes, detail on doing that with NMC1 devices is outlined here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156099 You use iplist.txt very similarly to the NMC2 devices. You download the SFSUMX372 and the wizard/utility is available in that .exe you extract the files from.

3.) What version do you have on there now? There are no known issues beyond if you are on firmware v1.X, and want to go to the latest, you need to put AOS 2.0.2 on, then continue with the newest AOS and application. Other than that, sometimes the wizard utility may fail if your NMC takes too long to boot up and continue loading the second file or if you have a really slow network connection. I'd personally recommend you only do groups of 5-10 cards at a time to keep an eye on things if you won't have physical access. Some of the network issues may be unpredictable so if you won't have physical access, small groups would be good. Most of the time, you can still get to the device remotely and would just have to re-run the wizard or manually FTP the upgrade which can be done remotely still.

Let us know if you have any other questions. Hope that helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:46 AM

0 Likes
0
1585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:46 AM

This reply was originally posted by Angela on APC forums on 6/23/2015


Hi Ryan,

1.) It depends on the UPS/device it goes in. Let's assume Smart-UPS - it would be AOS 3.7.3/sumx application v3.7.2. Look for part number SFSUMX372 on the firmware download page. AP9617/18/19 would always use the same firmware. I can't think of a time that they wouldn't when used in a UPS.

2.) Yes, detail on doing that with NMC1 devices is outlined here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156099 You use iplist.txt very similarly to the NMC2 devices. You download the SFSUMX372 and the wizard/utility is available in that .exe you extract the files from.

3.) What version do you have on there now? There are no known issues beyond if you are on firmware v1.X, and want to go to the latest, you need to put AOS 2.0.2 on, then continue with the newest AOS and application. Other than that, sometimes the wizard utility may fail if your NMC takes too long to boot up and continue loading the second file or if you have a really slow network connection. I'd personally recommend you only do groups of 5-10 cards at a time to keep an eye on things if you won't have physical access. Some of the network issues may be unpredictable so if you won't have physical access, small groups would be good. Most of the time, you can still get to the device remotely and would just have to re-run the wizard or manually FTP the upgrade which can be done remotely still.

Let us know if you have any other questions. Hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

ryan.schwellenbach_apc
Ensign ryan.schwellenbach_apc
Ensign

Posted: ‎2021-07-08 12:46 AM

0 Likes
0
1584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:46 AM

This was originally posted on APC forums on 6/25/2015


Angela,

All of our GEN1 cards are v3.1.3 and above. I will download the firmware upgrade utility and try a few at a time. Thanks for your help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.