Windows 7 Pro desktop with SUA2200RM

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Windows 7 Pro desktop with SUA2200RM
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

0 Likes
4
1976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

Windows 7 Pro desktop with SUA2200RM

Hi, I have a Windows 7 Pro desktop connected to a SUA2200RM UPS with an APC smart serial cable 940-0024. I installed the Powerchute Business Edition Agent (only) Single node which came with the UPS (no Server section and no Console) and it went very smoothly but I was surprized to see afterward that (apparently) I can only access the interface to set my options and check status via The Web/Cloud.

Is this normal? Seems Odd to me. I'd much rather be able to set my options and see status on my screen directly with info from the smart cable without having to go on the Internet. If this is normal for the business edition is there a different Powerchute edition that will work with this UPS - like Personal Edition perhaps?

I have only one desktop and one UPS and there is no network. What do you recommend for the most simple setup with as few bells and whistles as possible.  Also I'd be just as happy if, in a power failure, the computer was simply shut down (not hibernated) and stayed off even when mains power is restored.

Later on, I would also like to connect a second desktop to the same UPS perhaps using the AP9607 interface expander and a simple signal cable. Will this work?

I'd appreciate any help I can get. Thank you

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • computer
  • for
  • setup
  • simple
  • single
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

0 Likes
0
1976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

Alan,

PowerChute runs a web service on your computer. It is similar to the applications that are used to host web sites but it is restricted to PowerChute. A simple why to verify this is to disconnect your computer from your home / work network. Launch your favorite web browser and type in this address https://127.0.0.1:6547 You may see a message that state the site is not safe just ignore that and continue to the site. You will be able to log into the PowerChute Agent.

BTW: the address 127.0.0.1 is an internal IP address used by computers. If you would like more info on 127.0.0.1 please check out this link.http://www.howtogeek.com/126304/why-is-the-localhost-ip-127.0.0.1/

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

0 Likes
0
1977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

Alan,

When connecting to the PowerChute Agent via Internet Explore, Firefox etc you are not connection to the internet. PowerChute is running as a web application on the computer itself. There is no connection to the web unless your computers network is open to the web.

To answer the second question, yes, you can use the AP9607 with the SUA to connect a second system.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

0 Likes
0
1978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

Thankyou for your reply Bill but I don't see how that can be so. Can you please explain? This is a web application (only slightly different from a web site) and as I understand it, data is going back and forth between my computer and APC's server. If I unplug my Internet modem, its not going to communicate.

The reason for my concern of course is that 75% of all hacking attacks are carried out via web apps.

thanks,

Alan

  • Tags:
  • agent
  • PowerChute
  • setup
Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

0 Likes
0
1978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

i'm pretty sure that your browser is talking to a web server running on your computer as part of the PowerChute install. APC does offer remote monitoring for some products, but I believe that is an extra-cost option.

I would expect (but don't know for sure) that the web server is restricted to either the PC it is running on, or the local LAN only (in other words, it doesn't respond to requests from the "outside world").

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

0 Likes
0
1977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:47 AM . Last Modified: ‎2024-02-29 11:02 PM

Alan,

PowerChute runs a web service on your computer. It is similar to the applications that are used to host web sites but it is restricted to PowerChute. A simple why to verify this is to disconnect your computer from your home / work network. Launch your favorite web browser and type in this address https://127.0.0.1:6547 You may see a message that state the site is not safe just ignore that and continue to the site. You will be able to log into the PowerChute Agent.

BTW: the address 127.0.0.1 is an internal IP address used by computers. If you would like more info on 127.0.0.1 please check out this link.http://www.howtogeek.com/126304/why-is-the-localhost-ip-127.0.0.1/

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore