Power on Group Delays after return of AC power

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power on Group Delays after return of AC power
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:46 AM . Last Modified: ‎2024-02-29 11:02 PM

0 Likes
2
1344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:46 AM . Last Modified: ‎2024-02-29 11:02 PM

Power on Group Delays after return of AC power

I am using an SMX1500 (with 9630) with with a Linux box running apcupsd (USB control). When AC power is removed, the linux box shuts down, commands the UPS to shut down and all goes well. However, when the power is restored, all groups come on simultaneous rather than folowing the prescribed group delay sequence. When the UPS is powered on using the front panel button, the sequence is executed. I need the sequence to be obeyed no matter how the UPS is comes back on. Is there a configuration that needs to be set to make this so.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-08 12:46 AM . Last Modified: ‎2024-02-29 11:02 PM

0 Likes
0
1344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:46 AM . Last Modified: ‎2024-02-29 11:02 PM

These UPSes have the capability of rebooting with or without on delays. I think the NMC always uses them by default, so using an NMC and PCNET may be enough. It's interesting that the UPS' USB or Modbus implementation differs. Or maybe that's just what APCUPSd commands.

*edit* Nevermind, I missed the question of whether the on delay happens before or after waiting for AC. I talked with one UPS engineer who seems to think as long as the reboot has been commanded with on delays, the delays happen after waiting for AC.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:46 AM . Last Modified: ‎2024-02-29 11:02 PM

0 Likes
0
1344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:46 AM . Last Modified: ‎2024-02-29 11:02 PM

Brian,

It looks like APCUPSD is telling the SMX to reboot. After the power off delay is honored the power on delay immediately starts a countdown and the outlet groups all start up when AC is restored. I checked the APCUPSD Mail List and did not see a similar listing. I suggest you post this issue there. It would not surprise me if one of the group members has seen this and found a work around.

A work around that should work if your UPS has a Network Management Card (NMC) is you can set APCUPSD up with pcnet communication. Disable KillDelay in APCUPSD and configure start up / shut down using the NMC outlet group controls.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-08 12:46 AM . Last Modified: ‎2024-02-29 11:02 PM

0 Likes
0
1345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:46 AM . Last Modified: ‎2024-02-29 11:02 PM

These UPSes have the capability of rebooting with or without on delays. I think the NMC always uses them by default, so using an NMC and PCNET may be enough. It's interesting that the UPS' USB or Modbus implementation differs. Or maybe that's just what APCUPSd commands.

*edit* Nevermind, I missed the question of whether the on delay happens before or after waiting for AC. I talked with one UPS engineer who seems to think as long as the reboot has been commanded with on delays, the delays happen after waiting for AC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of