AP8653 Display Upgrade / Repair

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP8653 Display Upgrade / Repair
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
MorneMeintjes
Ensign MorneMeintjes
Ensign

Posted: ‎2025-03-27 07:50 AM

0 Likes
1
550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-27 07:50 AM

AP8653 Display Upgrade / Repair

Good Afternoon

 

I have a AP8653 it has 2 faults. the firs was the power supply that we fixed.

The second is the display, its blank and the PDU stay idle.

Using a display from a AP8953, the pdu activates and open all banks.

 

I see SE offers a display upgrade for the 0J-0G-9470 and 0J-0M-81332

 

But i'm not sure what display module I have and and what will be the replacement would be.

 

In fact I cant see any difference between the display for the AP8653 and the AP8953.

 

I want to upgrade to the latest hardware and firmware.

So my customer, sees the value in our services.

 

Best Regards

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Datacenter Accessories
  • Datacenter Netbotz & Monitoring
  • Datacenter Racks & Cooling
  • Datacenter UPS
  • Rack Accessories & Cooling
  • Racks
  • Server Room & Data Center Design Best Practices
  • UPS Management Devices & PowerChute Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-04-08 12:36 AM

0 Likes
0
496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-08 12:36 AM

Hello,

 

Customers receive AP8xxx/AP7xxx PDU's with an embedded NMC3. With the decommissioning of the NMC2, certain model AP8xxx PDU's will have their display upgraded to the NMC3. Units that shipped with an NMC2 will not support firmware for an NMC3 display module.


If an NMC3 is installed in a PDU that shipped with an NMC2 module, the following symptoms might occur:
The PDU does not show the correct hardware configuration data
The "overload" LED will be always lit
The unit will improperly measure variable data (amperage, voltage, etc)

 

If an NMC2 module is installed in a PDU that shipped with an NMC3 module, the PDU will no longer function.

 

for AP8653 beginning of the serial ZA2242022174,NMC 3 is built in in the Rpdu display

so first verfiy if NMC 2 based display 0J-0G-9470 is installed in the units ,if yes,then do not attempt to replace it with the new NMC3 display 0N-1642 as it causes Rpdu display communication issues and it is required to replace the entire Rpdu as the NMC2 based display is discontinued

 

If the Rpdu is equipped with NMC 3 based display beginning from serial ZA2242022174 and after then if there is a display issues you can replace only the NMC3 display 0N-1642 without issue and the latest firmware is available on our website 

 

firmware for NMC2 7.1.4 are available below 

https://www.se.com/uk/en/download/document/APC_RPDU2G_714_EN/

 

and NMC3  2.5.2.3  based display are available for upgrade as a free update, SNS tool license is required to update this NMC platform to version 3.x.x 

 

Regards,

 

Karim

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-04-08 12:36 AM

0 Likes
0
497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-08 12:36 AM

Hello,

 

Customers receive AP8xxx/AP7xxx PDU's with an embedded NMC3. With the decommissioning of the NMC2, certain model AP8xxx PDU's will have their display upgraded to the NMC3. Units that shipped with an NMC2 will not support firmware for an NMC3 display module.


If an NMC3 is installed in a PDU that shipped with an NMC2 module, the following symptoms might occur:
The PDU does not show the correct hardware configuration data
The "overload" LED will be always lit
The unit will improperly measure variable data (amperage, voltage, etc)

 

If an NMC2 module is installed in a PDU that shipped with an NMC3 module, the PDU will no longer function.

 

for AP8653 beginning of the serial ZA2242022174,NMC 3 is built in in the Rpdu display

so first verfiy if NMC 2 based display 0J-0G-9470 is installed in the units ,if yes,then do not attempt to replace it with the new NMC3 display 0N-1642 as it causes Rpdu display communication issues and it is required to replace the entire Rpdu as the NMC2 based display is discontinued

 

If the Rpdu is equipped with NMC 3 based display beginning from serial ZA2242022174 and after then if there is a display issues you can replace only the NMC3 display 0N-1642 without issue and the latest firmware is available on our website 

 

firmware for NMC2 7.1.4 are available below 

https://www.se.com/uk/en/download/document/APC_RPDU2G_714_EN/

 

and NMC3  2.5.2.3  based display are available for upgrade as a free update, SNS tool license is required to update this NMC platform to version 3.x.x 

 

Regards,

 

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.