5kVA UPS Self-Test Issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 5kVA UPS Self-Test Issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:49 AM . Last Modified: ‎2024-03-06 12:12 AM

0 Likes
2
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:49 AM . Last Modified: ‎2024-03-06 12:12 AM

5kVA UPS Self-Test Issue

Dear experts,

I'm having some issues with self-test on my 5kVA Online UPS.

I wanted to disable automatic self-test and have done so via NMC interface. After monitoring for a period of time I noticed that from time to time Self-Test was automatically perform.

I noticed output being turned off for no reason:

29.10.2012 04:18:24 UPS: The output power is turned off.
29.10.2012 04:18:24 UPS: aborted via front panel due to invalid state a self-test.
29.10.2012 04:18:23 UPS: Started a self-test.


There are times, self-test being performed twice a day.

11.10.2012 09:17:18 UPS: passed via management device a self-test.
11.10.2012 09:17:11 UPS: Started a self-test.
11.10.2012 09:16:27 UPS: passed via management device a self-test.
11.10.2012 09:16:18 UPS: Started a self-test.


My UPS Model: SURTD5000RMXLI

NMC Model: AP9631

Name: sumx
Version: v5.1.6

Name: aos
Version: v5.1.6

Name: bootmon
Version: v1.0.2


Urgently in need of help !

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • network_management_card
  • NMC
  • PowerChute
  • shutdown
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:49 AM . Last Modified: ‎2024-03-06 12:11 AM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:49 AM . Last Modified: ‎2024-03-06 12:11 AM

can you give me the first several digits of the serial number on these UPSs so i know how old they are? i.e. something like JS1035. In the NMC, this is located under UPS tab->About. i also would like the UPS firmware from this screen.

I asked someone on the UPS side about this and they said:

In looking through the logs, the UPS is definitely not actually switching to battery for them. And the only time it appears that it actually turned off the load was during a legit input power issue when it eventually drained the batteries. I would STRONGLY suggest leaving self test enabled as it can lead to swollen batts, dropped loads, etc - All kinds of bad things.
the next thing is to see how old the UPS/batteries are. if they are not the original batteries, can you tell me how old they are?

my thought is its either erroneous messages or potential quick transfers to battery and being reported as a self test. but i need the UPS age, firmware, and battery age to do anything further to investigate a root cause.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:49 AM . Last Modified: ‎2024-03-06 12:11 AM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:49 AM . Last Modified: ‎2024-03-06 12:11 AM

could you please provide config.ini and data.txt files as well? instructions are at FA156131 @ http://www.apc.com/site/support/index.cfm/faq/ if you need help getting the full versions. a full version of event.txt may help as well.

keep in mind, depending on your setting, the UPS can also do a self test everytime it is turned on so maybe you put "at start up" for the setting? config.ini will help me verify.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:49 AM . Last Modified: ‎2024-03-06 12:11 AM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:49 AM . Last Modified: ‎2024-03-06 12:11 AM

can you give me the first several digits of the serial number on these UPSs so i know how old they are? i.e. something like JS1035. In the NMC, this is located under UPS tab->About. i also would like the UPS firmware from this screen.

I asked someone on the UPS side about this and they said:

In looking through the logs, the UPS is definitely not actually switching to battery for them. And the only time it appears that it actually turned off the load was during a legit input power issue when it eventually drained the batteries. I would STRONGLY suggest leaving self test enabled as it can lead to swollen batts, dropped loads, etc - All kinds of bad things.
the next thing is to see how old the UPS/batteries are. if they are not the original batteries, can you tell me how old they are?

my thought is its either erroneous messages or potential quick transfers to battery and being reported as a self test. but i need the UPS age, firmware, and battery age to do anything further to investigate a root cause.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore