Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

What is the difference between the motor control type SVC I and SVC V in ATV71?

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • Re: What is the difference between the motor control type SVC I and SVC V in ATV71?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
BJacqz Mentor
49
LeoLazzaro
LeoLazzaro Troubleshooter
16
PriscilaCunha22
PriscilaCunha22 Troubleshooter
15
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Start a Topic
Solved
DCABANA
DCABANA
Explorer

Posted: ‎2022-10-21 08:43 AM . Last Modified: ‎2023-06-09 02:54 AM

1 Like
6
5797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-21 08:43 AM . Last Modified: ‎2023-06-09 02:54 AM

What is the difference between the motor control type SVC I and SVC V in ATV71?

What is the difference between the motor control type SVC I and SVC V in ATV71?

 

When do I need to select SVC I ? 

 

 

Labels
  • Labels:
  • Low Voltage AC Drives
  • Tags:
  • ATV71
  • motor control
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
LeoLazzaro
LeoLazzaro Troubleshooter
Troubleshooter

Posted: ‎2024-11-05 09:50 AM

0 Likes
1
4406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-05 09:50 AM

SVC U and SVC I are both open loop vector control . U fluxed by voltage and I fluxed by current.  

SVC U we can say that is the standard vector control with slip compensation , compatible for single and parallel motors( identical motors) . Autotune is mandatory to have good performance , but motor model inside is more flexible and less rigid.

SVC I it is used when high performance control is needed with single motor ( not possible to be used with motor in parallel ) , Motor model is adjusted more carefully  during autotune , optimizing the motor parameters=> basically we have a better motor model inside the drive => better control , it used for application like winder unwinder (torque control) , cranes , high speed or when high dynamic response is needed.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
dnordenberg1
dnordenberg1
Contributor

Posted: ‎2022-10-25 12:39 AM

0 Likes
0
5756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-25 12:39 AM

I always wondered the same thing. I think manual said something like SVC I is equal to the behaviour of the older ATV58 drives. But it does not say exactly what this "behaviour" is. As they decided to keep this "legacy" mode it has to have some positive effects too on some loads but I guess it's usage is probably very limited as SVC V was chosen as default.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

PCDTC
PCDTC
Contributor

Posted: ‎2024-04-27 05:20 AM

1 Like
0
4974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-27 05:20 AM

svci is used when you have high demand load with fluctuation, if the motor doesn't have encoder feedback the vfd will manage the current to keep the motor in working as much possible in the optimum current and torque based on motor standard specs . while svcv is only used to keep frequency and voltage control of simple applications like fans , conveyors , ... 

Reply

Link copied. Please paste this link to share this article on your social media post.

dnordenberg1
dnordenberg1
Contributor

Posted: ‎2024-05-01 03:05 AM

0 Likes
0
4959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-01 03:05 AM

Sounds like you are referring SVC U like a scalar mode but it is not, both are vector modes. But you might be right that SVC I has advantages in demanding applications. The manual that not say anything about that, only that SVC I mimics the behaviour of older ATV58 drives.

Reply

Link copied. Please paste this link to share this article on your social media post.

LeoLazzaro
LeoLazzaro Troubleshooter
Troubleshooter

Posted: ‎2024-11-05 09:50 AM

0 Likes
1
4406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-05 09:50 AM

SVC U and SVC I are both open loop vector control . U fluxed by voltage and I fluxed by current.  

SVC U we can say that is the standard vector control with slip compensation , compatible for single and parallel motors( identical motors) . Autotune is mandatory to have good performance , but motor model inside is more flexible and less rigid.

SVC I it is used when high performance control is needed with single motor ( not possible to be used with motor in parallel ) , Motor model is adjusted more carefully  during autotune , optimizing the motor parameters=> basically we have a better motor model inside the drive => better control , it used for application like winder unwinder (torque control) , cranes , high speed or when high dynamic response is needed.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

PCDTC
PCDTC
Contributor

Posted: ‎2024-11-05 11:44 PM

0 Likes
0
4375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-05 11:44 PM

svc- i uses current control and this is good for fluctuating loads 

svc- v uses voltage control which is good for torque and frequency precise control of loads 

in general voltage control for general loads is better , in heavy equipment current is better . 

Reply

Link copied. Please paste this link to share this article on your social media post.

dnordenberg1
dnordenberg1
Contributor

Posted: ‎2024-11-13 12:01 AM

In response to LeoLazzaro
0 Likes
0
4320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-13 12:01 AM

Interesting! I thought all kinds of vector control required single motor installations. But for me it doesn't matter much anyway since I dislike doing multi motors on a single VSD anyway 🙂 But I'm a bit curious on how the modern modells (320/600/900) hadle the SVC U/I choice since I think the option is now gone, is it SVC U only now?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore