Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Power Distribution IEC
  • Solutions for Motor Management
  • Label: Low Voltage AC Drives
Options
  • Mark all as New
  • Mark all as Read
  • Float this item to the top
  • Subscribe
  • Bookmark
  • Subscribe to RSS Feed
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Label: "low voltage ac drives"

View in: "Solutions for Motor Management" | Community

18 Posts | First Used: 2020-07-21

Top Labels
Top Labels
  • Alphabetical
  • Design & Build 23
  • Selection & sizing 20
  • Products 19
  • Low Voltage AC Drives 18
  • Digitalization 13
  • Training & How to 12
  • Energy Efficiency 11
  • Best Practice 8
  • Power Quality 7
  • Drives & Motor Control 3
  • Medium Voltage AC Drives 2
  • Smart Design & Engineering 2
  • Safety 2
  • Soft Starters 1
  • Connectivity 1
  • Material Handling 1
  • Previous
  • 1 of 2
  • Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Solutions for Motor Management

  • All
  • Solved
  • Unsolved
  • Unanswered
Solved
YOUNUS
/html/rank_icons/Crewman.png YOUNUS
Latest Reply: YOUNUS

Atv71

Dear sir We are using atv71 drive for crane application long travel purpose 4 motors connected together each motor 5.5 kw And vfd 30KW 2 Motors near the panel and motors 30 meters faraway When we start...
Power Distribution IEC Solutions for Motor Management
293
0
6
2023-03-26
Solved
AGuiver
AGuiver
Latest Reply: BJacqz

Alt12 remote run signal

Hi- I’ve got an atv12 inverter to run a three phase pump from single phase supply. Runs as expected in local- I’m running it via a remote key switch. So set to remote as per the manual. ( +24v to Ll1- ...
Power Distribution IEC Solutions for Motor Management
157
0
1
2023-02-27
Solved
TCRWater
TCRWater
Latest Reply: LeoLazzaro

Hour Meter on Altivar 61 not working

Hello, I have an Altivar 61 running a deep well submersible pump. It's working fine however the hour meter has stopped working on it. The meter has stopped at 65535 hrs. This happened a couple years ag...
Power Distribution IEC Solutions for Motor Management
302
0
2
2023-03-27
Solved
Flt
Flt
Latest Reply: BJacqz

ATV 320 - Why the BLF fault does not deactivate relay r1 w...

ATV 320 - Why the BLF fault does not deactivate relay r1 which was set to FLT?
Power Distribution IEC Solutions for Motor Management
213
0
1
2022-12-20
Ayesh
Ayesh
Latest Reply: BJacqz

Atv 312 drive Opf fault

Drive fault output side is OK. But fault is active.
Power Distribution IEC Solutions for Motor Management
567
0
2
2020-07-21
SESA161069_EF33
/html/rank_icons/Lieutenant.png SESA161069_EF33 /html/rank_icons/SE-Employee.png
Latest Reply: BJacqz

ATV motor trip

Hi, an existing installation is using ATV600 and ATV900 models. To implement a load shedding function, we need to be able to trip the motor in case of necessity. It there any precaution and/or checks...
Power Distribution IEC Solutions for Motor Management
215
0
1
2022-11-07
Sanderus
Sanderus
Latest Reply: Kevin_McDonald

Speed control with two potentiometer on ATV 930 drive

I have connected two 10kohm poti on AI1 and AI2 and high speed contact on DI3. I want control speed from poti 1 connected to AI1 in normal operation and from poti 2 connected to AI2 when DI3 is active....
Power Distribution IEC Solutions for Motor Management
160
0
1
2022-12-14
Solved
kanthavel3991
kanthavel3991
Latest Reply: Farooq8899

atv320 drivers show fault 'rdy'

Power Distribution IEC Solutions for Motor Management
306
0
2
2023-02-08
Gregory_Meunier
/html/rank_icons/Lieutenant_JG.png Gregory_Meunier /html/rank_icons/SE-Employee.png
Latest Reply: BJacqz

VSD contribution to upstream fault

Hi, I am looking for the fault contribution from Altivar 680 VSD in the context of a short-circuit calculation on a plant network (by IEC 60909 method). This model is known to have Active Front End, s...
Power Distribution IEC Solutions for Motor Management
214
0
1
2022-12-21
mark.lawrence.at.cseinc.com
mark.lawrence.at.cseinc.com
Latest Reply: BJacqz

Modbus port

can the one of the modbus ports on the Altivar 630 function like a Uni-telWay/Modbus com card on the Altivar 61? I am replacing a Altivar 61 that uses theUni-telWay/Modbus com card with anAltivar 630 a...
Power Distribution IEC Solutions for Motor Management
153
0
2
2023-01-10
Aleksandr92
Aleksandr92
Latest Reply: BJacqz

Altivar 930

What to do if the password has been lost?
Power Distribution IEC Solutions for Motor Management
148
0
2
2022-12-26
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc