Security Expert integration to EBO via SmartConnector

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Security Expert integration to EBO via SmartConnector
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
Start a Topic
Elt_Andrius
Ensign Elt_Andrius
Ensign

Posted: ‎2021-03-16 01:50 AM

0 Likes
11
5769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-16 01:50 AM

Security Expert integration to EBO via SmartConnector

Hello,

 

I'm struggling with Security Expert integration to EBO via SmartConnector.

I installed smart connector, attached a license, created a EWS server.

On EBO I created EWS interface, communication is online with smartconnector.

But how to read all the values from smart security to smartconnector so I could read them in EBO?

 

I'm using 2.4.17 smart connector

and EBO 3.2.2

 

Maybe someone has some advise what to do next?

Thank you.

 

@David_Kendrick 

@Mahmoud_Sayed 

Tags (5)
  • Tags:
  • ebo
  • english
  • integration
  • SecurityExpert
  • smartconnector
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
Elt_Andrius
Ensign Elt_Andrius
Ensign

Posted: ‎2021-03-16 02:13 AM

0 Likes
0
5768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-16 02:13 AM

Hi @ChrisLeijtens .

I saw your post about smartconnector for Security Expert.

Maybe you have some information about it?

 

Thank you

Andrius

Tags (1)
  • Tags:
  • english
Reply
David_Kendrick
Admiral David_Kendrick Admiral
Admiral

Posted: ‎2021-03-16 04:42 AM

0 Likes
9
5749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-16 04:42 AM

 

Hi @Elt_Andrius 

 

Can you please clarify what data you do not currently have?

Are you seeing the EWS points which you need and just want to know how to bring this into EBO or are data points missing at the EWS stage?

 

Regards

 

Dave K

 

 

Tags (1)
  • Tags:
  • english
Reply
Elt_Andrius
Ensign Elt_Andrius
Ensign

Posted: ‎2021-03-16 04:54 AM

0 Likes
8
5747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-16 04:54 AM

Hello @David_Kendrick ,

 

I need to know how to launch SmartConnector. Because on my site Security expert and EBO is done by different companies. And other company is new with Schneider security expert system, specially when it we talk about integration.

So I need to know if they need to do something more in Security expert? Do they need to install additional EWS services for example.

And from my side how should I set up a SmartConnector? Do I need some extra extension so I could get all points from security expert.

I missing some information about this integration via SmartConnector. All I have found is about older integration using EWS and SOAP without SmartConnector.

 

Regards,

Andrius

 

Tags (1)
  • Tags:
  • english
Reply
David_Kendrick
Admiral David_Kendrick Admiral
Admiral

Posted: ‎2021-03-16 05:25 AM

0 Likes
7
5744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-16 05:25 AM

 

Hi @Elt_Andrius 

 

So you do not actually have the Smart Connector installed and running yet?

The Smart Connector is currently undergoing Beta Testing so the full product and documentation is not yet released.

 

I would suggest that you either wait until its official release/documentation etc or see if you can join the Beta program at this late stage.

 

Regards

 

Dave K

 

Tags (1)
  • Tags:
  • english
Reply
Elt_Andrius
Ensign Elt_Andrius
Ensign

Posted: ‎2021-03-16 05:33 AM

0 Likes
6
5742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-16 05:33 AM

I see. So I already installed SmartConnector and started EWS server. From EBO I connected to this SmartConnector EWS server. The communication status in EBO is online. Everything seems okey. But I'm missing all the points from security expert. I don't know how to start this processor so I could transfer all the points.

 

Is there a possibility to join this Beta program testing. Because this project is going to it's end and I don't think that I can wait more longer.

 

Best regards

Andrius

Tags (1)
  • Tags:
  • english
Reply
ChrisLeijtens
Lieutenant ChrisLeijtens Lieutenant
Lieutenant

Posted: ‎2021-03-16 07:56 AM

0 Likes
0
5727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-16 07:56 AM

Looks like the SmartConnector will be released next month but not confirmed yet.

Tags (1)
  • Tags:
  • english
Reply
Mike_Bielby
Lt. Commander Mike_Bielby Lt. Commander
Lt. Commander

Posted: ‎2021-03-16 09:07 AM

1 Like
4
5719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-16 09:07 AM

Hi,

The official SX Smart Connector Beta program is closed and now we are working towards an end of this Quarter release. So far so good.  What I will do is add you to the MS Teams SX Smart Connector Beta channel and you can ask your questions there as there are people there that can help with your immediate issues.

 

Best regards,

Mike 

Tags (4)
  • Tags:
  • Beta Program
  • english
  • security expert
  • smart connector
Reply
Elt_Andrius
Ensign Elt_Andrius
Ensign

Posted: ‎2021-03-16 01:54 PM

0 Likes
0
5711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-16 01:54 PM

@Mike_Bielby  Thank you.

My server have changed. My email is andrius@eltko.lt

 

Best regards,

Andrius

Tags (1)
  • Tags:
  • english
Reply
Elt_Andrius
Ensign Elt_Andrius
Ensign

Posted: ‎2021-03-17 12:43 AM

0 Likes
1
5700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-17 12:43 AM

I found your post about step by step SmartConnector launching as a user guide. It was very useful.

 

I have few question. Maybe you can answer me.

I installed software, copied extension files, attached license.

 

As I understand I need to create and start EWS server from the extension ? This EWS server is where my EBO will connect right?

 

Then I need to set up a processor from the extension? In these settings in Security Expert setting are default ? Or I need to active soap endpoint and create separate user for this communication? 

 

And this EWS server is the same server that I created on SmartConnector portal, where all data will be stored?

 

Thank you

Andrius

Attachments
Tags (1)
  • Tags:
  • english
Reply
David_Kendrick
Admiral David_Kendrick Admiral
Admiral

Posted: ‎2021-03-17 07:10 AM

1 Like
0
5689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-17 07:10 AM

 

Hi @Elt_Andrius 

 

You need to address all your Smart Connector questions to the MS Teams SX Smart Connector Beta channel that @Mike_Bielby  mentioned in his previous post for the time being.......

 

This is where you are most likely to receive support from people who have just completed the Beta program and have experience of setting up the integration.  Of course once the Smart Connector is released you can continue to post your Smart Connector questions here and raise PSS cases with your local CCC..

 

Regards

 

Dave K

 

 

Tags (1)
  • Tags:
  • english
Reply
Elt_Andrius
Ensign Elt_Andrius
Ensign

Posted: ‎2021-03-18 11:39 PM

0 Likes
0
5679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-18 11:39 PM

Hi @Mike_Bielby 

 

I didn't receive a invitation to this channel. Could you send it to my email - andrius@eltko.lt

 

 Thank you,

Andrius

Tags (1)
  • Tags:
  • english
Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore