Scapack470 Modbus slave

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • Scapack470 Modbus slave
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
75
BevanWeiss
Spock BevanWeiss
20
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Solved
Noel
Crewman Noel
Crewman

Posted: ‎2021-11-08 12:45 AM

0 Likes
1
786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-08 12:45 AM

Scapack470 Modbus slave

Hi, I would to ask procedure using remote connect software to read modbus data from a PLC, i saw a tutorial but it was the  scapack 32 using the old software..https://youtu.be/i_zQbVwXpa4

 

Thanks 

Labels
  • Labels:
  • RTU
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2021-11-08 07:42 AM

0 Likes
0
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-08 07:42 AM

Hello Noel,

 

When you wrote "PLC" I presume that you mean a SCADAPack x70 type RTU.  The comments below depend on that. Also, you did not state whether you require Ethernet or serial interface. These comments presume that either might be needed.

 

To allow an external device to communicate with an x70 SCADAPack via Modbus requires a few steps be performed, to configure the desired objects with Modbus addresses and configure the port.

 

1) While OFFLINE, right-click on the SCADAPack x70 Controller DeviceDTM and open the Additional Functions menu

2) Select Project Settings and ensure that Modbus IP Servers OR Modbus RTU Server is selected 

NOTE: This feature is enabled by default, so we're just double-checking here...

 

3) On the main Configuration - SPx70 Controller tab, select the Objects tab, then Object Configuration

4) Expand the list of Analog, Digital and Counter objects and open an object that will communicate with the polling device.

5) Select the Modbus tab, enter a Modbus register and data type. Eg for a counter input you might enter 40001 and UINT.

6) Perform this same step with all other objects that must communicate via Modbus.

7) If desired to perform any scaling this can be done on the Basic tab. (eg for analog inputs)

NOTE: if configuring multiple items in a row, you can use the Next > button to move quickly between them.

8/ Once done, press Apply to accept the edits

 

9) Change to the Configuration tab, select the desired Ethernet or serial port and configure it appropriately.

10) Expand the Modbus section, select Server, and set the Unit Identifier (Station address) as required.

11) Apply these changes made to the RTU.

12) Save the configuration, go Online, then Write the changed configuration to the RTU

 

Of general interest is this YouTube video series which presents a basic introduction to RemoteConnect and the Logic Editor.

https://www.youtube.com/watch?v=EVwk7ADhCqE&list=PLa7UGrWOTyjlyww9RcENfi8u9i8SKPZ0c&index=16

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2021-11-08 07:42 AM

0 Likes
0
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-08 07:42 AM

Hello Noel,

 

When you wrote "PLC" I presume that you mean a SCADAPack x70 type RTU.  The comments below depend on that. Also, you did not state whether you require Ethernet or serial interface. These comments presume that either might be needed.

 

To allow an external device to communicate with an x70 SCADAPack via Modbus requires a few steps be performed, to configure the desired objects with Modbus addresses and configure the port.

 

1) While OFFLINE, right-click on the SCADAPack x70 Controller DeviceDTM and open the Additional Functions menu

2) Select Project Settings and ensure that Modbus IP Servers OR Modbus RTU Server is selected 

NOTE: This feature is enabled by default, so we're just double-checking here...

 

3) On the main Configuration - SPx70 Controller tab, select the Objects tab, then Object Configuration

4) Expand the list of Analog, Digital and Counter objects and open an object that will communicate with the polling device.

5) Select the Modbus tab, enter a Modbus register and data type. Eg for a counter input you might enter 40001 and UINT.

6) Perform this same step with all other objects that must communicate via Modbus.

7) If desired to perform any scaling this can be done on the Basic tab. (eg for analog inputs)

NOTE: if configuring multiple items in a row, you can use the Next > button to move quickly between them.

8/ Once done, press Apply to accept the edits

 

9) Change to the Configuration tab, select the desired Ethernet or serial port and configure it appropriately.

10) Expand the Modbus section, select Server, and set the Unit Identifier (Station address) as required.

11) Apply these changes made to the RTU.

12) Save the configuration, go Online, then Write the changed configuration to the RTU

 

Of general interest is this YouTube video series which presents a basic introduction to RemoteConnect and the Logic Editor.

https://www.youtube.com/watch?v=EVwk7ADhCqE&list=PLa7UGrWOTyjlyww9RcENfi8u9i8SKPZ0c&index=16

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of