[Imported] Convert Isagraf 3.5 program to Scadapack Workbench

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Convert Isagraf 3.5 program to Scadapack Workbench
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-06 02:48 AM

0 Likes
5
6645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-06 02:48 AM

[Imported] Convert Isagraf 3.5 program to Scadapack Workbench

>>Message imported from previous forum - Category:SCADAPack RTU<<
User: Cesarin, originally posted: 2018-11-23 06:19:56 Id:325
I have an application in Isagraf 3.5 (.pia file) and it is installed in a Scadapack ES. I want to upgrade the hardware to Scadapack 357E and convert the program to Scadapack Workbench. So I have few questions:

1. Since the existing hardware is Scadapack ES, do I need a configuration file (Scadapack E Configurator) in addition to the .pia file or Isagraf already have the configuration?
2. How do I convert the .pia file to Scadapack Workbench target 5? So far I was able convert the .pia file to Scadapack Workbench target 3. But when I compile the program it give some errors due to some functions blocks are part of Target 5 only.
3. Is it possible to convert a Scadapack Workbench target 3 program to target 5?

Thanks.

Labels
  • Labels:
  • RTU
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-06 02:49 AM

0 Likes
4
6648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-06 02:49 AM

>>Responses imported from previous forum


Reply From User: dmercer, posted: 2018-12-07 05:23:47
You always require a separate isagraf configuration file for the SCADAPacks, this applies to the old Isagraf3.5 and to Workbench.

Unfortunately, there is no way to automatically convert a target 3 application to a target 5 application, but there are some techniques to make a manual conversion easier.

Attached is the conversion guide, which gives the basic details on how to do the conversion. The biggest pain that I found was redoing the I/O configuration. You may be able to save some time on this by setting up the I/O boards (empty), configuring the variable wiring in the spreadsheet of exported variables, then reimporting the variables.

 


Attached file: (editor/61/b43b4e27ovni.docx), SCADAPack 535E Migration Guide v1.0.docx File size: 1729870


Reply From User: Cesarin, posted: 2018-12-07 16:31:47
Thanks Dmercer. I did some progress moving the program to Target 5. Now I'm looking at the SP E configurator and wonder if there is a way to export/import Points. I have the existing Scadapack ES configuration file.

Thanks


Reply From User: dmercer, posted: 2018-12-10 21:44:03
The configurator files can be opened in a text editor. You can copy and past the point configuration between them that way.

Eg.
PC DU
RN 2070
PDC C1B CL CL
MRA 2070 1 0
LGT N
TE
is a binary point

RN 12604
OBT 40 1
PDC C0S CL CL
LGT N N N N N N N N N N
TE
is an analog point

PC CI
RN 0
TE
is a counter point


Reply From User: Cesarin, posted: 2018-12-11 17:28:25
That trick is handy. I got another question. I created my own function block in SP Workbench. Basicalli copying valuues from one variable to another. But there is one where I need to use a standar function block (addition). The program is compiled with no errors. The program is downloaled into the RTU with no errors as well. But the status LED is flashing and in SP configurator shows error: "Unknown TIC code". And seems it only happens when there is a standard function block in a customized function block.

See Answer In Context

  • Tags:
  • IsaGraf version 3.5 technical support
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-06 02:49 AM

0 Likes
4
6649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-06 02:49 AM

>>Responses imported from previous forum


Reply From User: dmercer, posted: 2018-12-07 05:23:47
You always require a separate isagraf configuration file for the SCADAPacks, this applies to the old Isagraf3.5 and to Workbench.

Unfortunately, there is no way to automatically convert a target 3 application to a target 5 application, but there are some techniques to make a manual conversion easier.

Attached is the conversion guide, which gives the basic details on how to do the conversion. The biggest pain that I found was redoing the I/O configuration. You may be able to save some time on this by setting up the I/O boards (empty), configuring the variable wiring in the spreadsheet of exported variables, then reimporting the variables.

 


Attached file: (editor/61/b43b4e27ovni.docx), SCADAPack 535E Migration Guide v1.0.docx File size: 1729870


Reply From User: Cesarin, posted: 2018-12-07 16:31:47
Thanks Dmercer. I did some progress moving the program to Target 5. Now I'm looking at the SP E configurator and wonder if there is a way to export/import Points. I have the existing Scadapack ES configuration file.

Thanks


Reply From User: dmercer, posted: 2018-12-10 21:44:03
The configurator files can be opened in a text editor. You can copy and past the point configuration between them that way.

Eg.
PC DU
RN 2070
PDC C1B CL CL
MRA 2070 1 0
LGT N
TE
is a binary point

RN 12604
OBT 40 1
PDC C0S CL CL
LGT N N N N N N N N N N
TE
is an analog point

PC CI
RN 0
TE
is a counter point


Reply From User: Cesarin, posted: 2018-12-11 17:28:25
That trick is handy. I got another question. I created my own function block in SP Workbench. Basicalli copying valuues from one variable to another. But there is one where I need to use a standar function block (addition). The program is compiled with no errors. The program is downloaled into the RTU with no errors as well. But the status LED is flashing and in SP configurator shows error: "Unknown TIC code". And seems it only happens when there is a standard function block in a customized function block.

  • Tags:
  • IsaGraf version 3.5 technical support
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-12-10 01:29 AM

In response to sbeadle
0 Likes
3
6597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-12-10 01:29 AM

Attached file.

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

HDP
Ensign HDP
Ensign

Posted: β€Ž2021-11-10 01:57 PM

In response to sbeadle
0 Likes
2
4488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-11-10 01:57 PM

Hello,

 

I would like to open up the old backups I have for the E serise RTUs. I have a *.pia and *.X8M files.

 

I am using windows 10 and can only open SCADA workbench target 5 applications. When I try to open the target 3 applications using ISAGRAF target 3 it shows error "Cant open project IO database". (I am not connected to RTU while I am doing this). Also the RTU has latest firmware.

 

I read the document to convert the traget 3 applications to target 5 requires the *.hie file. I am not sure how to get *.hie file as I only have *.pia and *.X8M files.

 

Is there a way to open the *.pia or *.X8M files?

 

Thank you

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: β€Ž2021-11-15 10:46 AM . Last Modified: β€Ž2021-11-15 12:58 PM

In response to HDP
1 Like
1
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-11-15 10:46 AM . Last Modified: β€Ž2021-11-15 12:58 PM

Hello again Hardik Patel,

 

As noted in your other post, your Tech Support team may be able to assist you with this issue.

 

Support for Australia, New Zealand, Pacific regions:

techsupport.pz@se.com

13 73 28 (13 SEAU)  inside Australia

0800 652 999 in side New Zealand

 

Alternately, support for Americas, Middle East and Asia is:

1-888-226-6876  or...

SupportTRSS@se.com

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

HDP
Ensign HDP
Ensign

Posted: β€Ž2021-11-15 08:17 PM

In response to Joel_Weder
0 Likes
0
4437
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-11-15 08:17 PM

Thank you Joel, I will contact the tech support πŸ™‚

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore