Dear Team,
I would like to know with Latest 474 controller how many Maximum 5606 IO Expansion module i can use.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-14 08:53 AM . Last Modified: 2021-07-14 09:08 AM
Hello Sameer,
The SCADAPack 47x datasheet (copy attached) lists the maximum number of expansion modules at 15. This is in the "Additional I/O" section near the bottom of page 6. Also, see note 7 at the bottom of the page about the possible requirement for additional power supplies.
A solid-state 5606 requires 400 mA, which at 5 volts on the bus is 2 watts. A relay version requires 600 mA, which is 3 watts. The 474's internal power supply could power one of the relay modules, or two of the solid-state type. Beyond that, external power supply would be required. The model 5103 power supply can provide 5 Vdc to the bus at 2 amps, or 10 watts total. So you'd need several 5103's to power 15 x 5606's.
Our new 6103 power supply, due to be released this month, has the same output capacity, but one additional benefit. It includes a 16-pin output bus connector for 5000 series modules, so there is no need to add a 20-to-16-pin adapter.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-14 08:53 AM . Last Modified: 2021-07-14 09:08 AM
Hello Sameer,
The SCADAPack 47x datasheet (copy attached) lists the maximum number of expansion modules at 15. This is in the "Additional I/O" section near the bottom of page 6. Also, see note 7 at the bottom of the page about the possible requirement for additional power supplies.
A solid-state 5606 requires 400 mA, which at 5 volts on the bus is 2 watts. A relay version requires 600 mA, which is 3 watts. The 474's internal power supply could power one of the relay modules, or two of the solid-state type. Beyond that, external power supply would be required. The model 5103 power supply can provide 5 Vdc to the bus at 2 amps, or 10 watts total. So you'd need several 5103's to power 15 x 5606's.
Our new 6103 power supply, due to be released this month, has the same output capacity, but one additional benefit. It includes a 16-pin output bus connector for 5000 series modules, so there is no need to add a 20-to-16-pin adapter.