Isagraf 3.55 Target 3 to Workbench Target 5 conversion Import issue

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • Isagraf 3.55 Target 3 to Workbench Target 5 conversion Import issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
SCADAPack Workbench Technician Tool & Utilities

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
HDP
Ensign HDP
Ensign

Posted: ‎2022-04-27 09:42 PM

0 Likes
2
3752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-27 09:42 PM

Isagraf 3.55 Target 3 to Workbench Target 5 conversion Import issue

Hello,

 

I have Isagraf 3.55 *.Hie file which I would like to import into workbench but it gives me error "Unsupported feature message true/ message false values: Remove unsupported values from an earlier work bench version"

 

I cannot find exact source of error and dont have any clue as where to look for.

 

Has anyone had this issue?

 

Thankyou.

Attachments
Labels
  • Labels:
  • RTU
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2022-04-28 02:53 PM

0 Likes
0
3728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-28 02:53 PM

Hello,

 

Unfortunately it is not possible to convert directly from an ISaGRAF application to a Workbench Target 5 application. You will first need to import your ISaGRAF 3.55 application into a Target 3 (CAM3) Workbench application, and then use a combination of manual operations to port the variables and logic sections into a Target 5 (CAM5) application. There's no easy way to convert between Target 3 and Target 5. The flowchart I have attached provides a rough procedure to follow.

 

Importing into Workbench Target 3 is fairly easy. After opening Workbench, create a New Project, then select Target 3 > Import & select "Import SCADAPack ISaGRAF 3 Project"   Enter a name for the project below, Browse to the desired storage location, then click OK. You will then be prompted to select the ISaGRAF appli.hie file.

 

Next you create a Target 5 application which will reside in Workbench at the same time as the Target 3 application, so you can copy directly between them. Right-click on Solution at the top of the Solution Explorer, then Add > New Project. This way you can create an identical Target 5 logic section structure and copy over the logic. 

 

A couple of notes however:

- Target 3 Variables must be exported to Excel, then converted to the same column structure as required by Target 5 before importing. To see the required Target 5 structure, just do an Export from the Target 5 app. It's a bit different.

- Quite a few function blocks are different between Target 3 and Target 5. You'll need to find these and re-create any logic that does not copy over successfully.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Attachments
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

RW_Support
Ensign RW_Support Ensign
Ensign

Posted: ‎2022-05-02 12:39 PM

1 Like
0
3611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-02 12:39 PM

Hello,

 

Although Joel is correct,

 

I believe the question may be flawed. It sounds like you are converting an ISaGRAF 3.55 standard application to a SCADAPack Workbench application. SCADAPack Workbench still uses a target 3 (or CAM 3) version when following the instructions in the manual for standard SCADAPacks (non-e)

 

You are seeing this error because some of the True/False fields for VALUE in Boolean variables in the ISaGRAF 3.55 project contain custom words. This is not supported in SCADAPack Workbench conversion.

 

Please check your program for all global and local Boolean values to see if there values for True/False as highlighted in the attached image. Delete the custom words, then build and save the project and re-import the .hei folder as per the manual. If you have further challenges it would be best to contact your local technical support representative or "SupportTRSS@se.com" shall you have additional questions regarding your project.

 

 

Attachments
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore