SCADA - Ethernet Radio Qs!

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • SCADA - Ethernet Radio Qs!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
cariebens
Crewman cariebens
Crewman

Posted: ‎2022-05-18 03:51 AM

0 Likes
2
1754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-18 03:51 AM

SCADA - Ethernet Radio Qs!

Heya all,

What ethernet radios are you guys using for your remote SCADA systems? (Water/Wastewater, Oil, etc)

Isn't there an inherent issue of broadcasts on the network that could potentially flood the network? Or is this remedied by proper network planning - managed switches, VLANs, access rules etc.

Looking for some ideas, or at least someone to throw some ideas off of.

Thanks

10.0.0.0.1 192.168.1.254
Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2022-05-18 08:44 AM

0 Likes
0
1740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-18 08:44 AM

I'll let others respond about their field experiences, but I can comment about the capabilities of our Trio Ethernet radios. 

 

Yes it is possible to easily overload an Ethernet radio network with traffic from an un-disciplined LAN. Consider that the LAN may be operating at 100 Mbps or even 1 Gbps, while the radios may be operating at well under 1 Mbps - in some cases as low as 8 kbps. We include features in the radios to help with this bottle-necking, including (depends on radio type):

 

- Spanning Tree typically disabled (can be enabled if required)

- Default filter type is "Allow ARP and Unicast" to ignore broadcast & multicast traffic

- Filters which allow many typical protocols to be either allowed or blocked

- Ability to filter based on port #, MAC or IP address

 

Also, QoS (quality of service) can be configured to ensure each protocol is configured with a maximum allowable data rate. 

 

I look forward to hearing from others about their actual experiences & lessons learned...

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-05-29 09:37 PM

0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-29 09:37 PM

We tend to use whatever the customer has ingrained, this has been 4RF (Aprisa SR/SR+), Trio radios (D,S,M,E,Q), and GE (MDS) [if we excluded other analogs].

 

When it comes to digital 'ethernet' radios it is harder to keep the traffic 'clean'.

Having it on a separate VLAN can be incredibly useful, but also makes troubleshooting that much more difficult.

As do things like firewall rules etc.

 

Definitely blocking multicast traffic (excluding ARP) can be helpful, certainly if you have Rockwell Multicast / EthernetIP IO devices on your network you'll want to give this special consideration.

You'll still tend to get quite a lot of spurious noise if you have PCs etc on the shared network, since they seem to ask for ARP resolution of email servers, domain controllers and lots of software update services very frequently.

This small traffic can have a surprisingly negative impact on a telemetry radio network, it can generate collisions, and just in general messes with the nice orderly seuencing of network traffic.

 

There are a range of things that can be done, like QoS (prioritising DNP3 / control traffic, and de-prioritising things like HTTP/HTTPS.. but you still need ARP to be prioritised or other things stop working in less graceful ways).

I would really recommend a high level network segmentation however.  That has the best chance of cleaning things up.

Using an RTU with multiple ports can be very helpful.

 

So my most preferred configuration is with something like the SCADAPack x70 series, and their three ethernet ports.

You can have 1 port dedicated for Radio comms, another port for PLC/IO network traffic comms, and if necessary the 3rd port for SCADA/HMI comms (if not already on the PLC/IO network).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore