We tend to use whatever the customer has ingrained, this has been 4RF (Aprisa SR/SR+), Trio radios (D,S,M,E,Q), and GE (MDS) [if we excluded other analogs].
When it comes to digital 'ethernet' radios it is harder to keep the traffic 'clean'.
Having it on a separate VLAN can be incredibly useful, but also makes troubleshooting that much more difficult.
As do things like firewall rules etc.
Definitely blocking multicast traffic (excluding ARP) can be helpful, certainly if you have Rockwell Multicast / EthernetIP IO devices on your network you'll want to give this special consideration.
You'll still tend to get quite a lot of spurious noise if you have PCs etc on the shared network, since they seem to ask for ARP resolution of email servers, domain controllers and lots of software update services very frequently.
This small traffic can have a surprisingly negative impact on a telemetry radio network, it can generate collisions, and just in general messes with the nice orderly seuencing of network traffic.
There are a range of things that can be done, like QoS (prioritising DNP3 / control traffic, and de-prioritising things like HTTP/HTTPS.. but you still need ARP to be prioritised or other things stop working in less graceful ways).
I would really recommend a high level network segmentation however. That has the best chance of cleaning things up.
Using an RTU with multiple ports can be very helpful.
So my most preferred configuration is with something like the SCADAPack x70 series, and their three ethernet ports.
You can have 1 port dedicated for Radio comms, another port for PLC/IO network traffic comms, and if necessary the 3rd port for SCADA/HMI comms (if not already on the PLC/IO network).