PowerLogic T300 - Can't read Modbus TCP/IP data from PowerLogic P3

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - Can't read Modbus TCP/IP data from PowerLogic P3
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic T300
product field
PowerLogic
PowerLogic P3

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Protection & Control
Start a Topic
Hoang_Phu
Ensign Hoang_Phu
Ensign

Posted: ‎2025-12-13 11:17 PM . Last Modified: ‎2025-12-16 01:39 AM

0 Likes
3
42
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-13 11:17 PM

PowerLogic T300 - Can't read Modbus TCP/IP data from PowerLogic P3

I can read successfully in Modbus tester and Scada system but I can't read Easergy T300. What am I doing wrong or missing? I have Virtual input 5 activated on the Easergy P3 relay.

ModBus100.jpgModbus101.jpgModbus102.jpgModbus103.jpgModbus104.jpgModbus105.jpgModbus106.jpgModbus107.jpgModbus108.jpgModbus109.jpg

 

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
  • Thumbnail of PowerLogic P3
    PowerLogic
    PowerLogic P3
View products (2)
Labels
  • Labels:
  • PowerLogic P3
  • PowerLogic T300
Tags (6)
  • Tags:
  • english
  • p3
  • PowerLogic P3
  • PowerLogic T300
  • t300
  • T300 Modbus TCP
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Karthik.P
Ensign Karthik.P Ensign
Ensign

Posted: ‎2025-12-15 01:09 AM

0 Likes
2
37
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-15 01:09 AM

Dear Hoang Phu

 

The configuration on P3 device is correct. 

Many of the Modbus master tools has codes implemented with zero. So, you need to reduce the registry number by one. For eg. If you registry one is 40358, then in the Modbus master tool you need to enter 40357

 

Regards

Karthik.P

Reply
Hoang_Phu
Ensign Hoang_Phu
Ensign

Posted: ‎2025-12-15 03:19 AM

0 Likes
1
22
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-15 03:19 AM

Thanks for the reply @Karthik.P 

I tried the method you suggested. I checked the register as 3459 and 3457. if the register was wrong, then one of the virtual inputs must have been read. That's why I thought that my connection settings might be wrong and asked you all. Or do I need to set a mask? Since the value I'm reading contains 0 and 1 values, I don't think I need to set a mask.

v1.jpg

 

Reply
Karthik.P
Ensign Karthik.P Ensign
Ensign

Posted: ‎2025-12-15 11:00 PM

0 Likes
0
21
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-15 11:00 PM

Dear Hoang Phu

 

Since it is ethernet connection, I don't think there will be as mistake in the connections. However, you can share the connection details to us to verify.

 

You are correct that there is no need for any masking. 

 

Some of the tools has Modbus implementation that starts from 0. So, it is common practice that we reduce the modbus register number by 1 and enter the reduced value into the SCADA system. For eg: The registry value of P3 device is 40358 which corresponds to virtual input 5 and in your SCADA system you need to enter the registry value as 40357. 

 

If you have tried the above and still not working, then I can connect on remote and support you

 

Regards

Karthik.P

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore