Dear All,
1. how to fix version number mismatch on relay vamp 52 ?
existing unit : vamp 52 V10.104
back up parameter : vamp 52 V10.134
2. What is the password on relay vamp 52 ?
Link copied. Please paste this link to share this article on your social media post.
Hi @Andhika_Amir
#2 The default password can be found from the user manual.
#1 You are trying to upload the V10.134 setting file to the relay with V10.104. That is not possible.
BR
-juha-
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi @Andhika_Amir
#2 The default password can be found from the user manual.
#1 You are trying to upload the V10.134 setting file to the relay with V10.104. That is not possible.
BR
-juha-