Programming ION Meter with Self Read Integrators

Power Monitoring and Energy Automation NAM

This forum is created for the exchange of information and open dialogue regarding electrical power monitoring and energy automation products and services. Participants will have access to downloadable material as well as chat opportunities with subject matter experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution NEMA
  • Power Monitoring and Energy Automation NAM
  • Programming ION Meter with Self Read Integrators
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
7
Michael_Neas
Ensign Michael_Neas Ensign
3
Robert_Lee
Admiral Robert_Lee Admiral
2
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic ION8650 series
product field
PowerLogic
PowerLogic ION7400 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Monitoring and Energy Automation NAM
Start a Topic
N4th4n13L
Lieutenant JG N4th4n13L Lieutenant JG
Lieutenant JG

Posted: ‎2022-01-28 01:11 PM

2 Likes
0
2591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-28 01:11 PM

Programming ION Meter with Self Read Integrators

The following instructions will help you setup your ION meter with end of day self reads. These are the cumulative registers that MV90 and other billing systems will use for your stop read, and setting them up as end of day reads will ensure that MV90 stop read is the energy read at end of day rather than time of interrogation.

 

First, the integrators used for stop reads are also commonly used by your meter displays, DNP and Modbus maps, and TOU energy frameworks. We can take 2 approaches to setting up the meter; create new self read integrator modules or re-map other existing frameworks and modules to different or new integrator modules.

 

Most ION frameworks use integrator modules 1, 2, 5, and 6 as the cumulative or stop read integrators when the load profile is data is downloaded. To convert the integrator modules to end of day self reads. Map the Update Outputs inputs register to the Clock 1 CL1 New Day output register. The register itself is still constantly integrating, but the outputs will only update at 24:00 each day.

 

 

If you want other displays, mappings, and frameworks to use a different register you’ll need to lookup their connections and re-map to the appropriate integrator module.

 

If you take the route of adding new integrator modules and setting them up for end of day self reads. You’ll also need to make sure the billing system is setup to use those integrators instead of the previous cumulative registers used for stop reads. For MV90 this is done through the encoder type field in MV90. For each channel you’ll need to specify the new integrator module number. For example, if you create 4 new integrators: Integrator 96 (kWh del), Integrator 97 (kWh rec), Integrator 98 (kVARh del), and integrator 99 (kVARh rec). The channel setup for kWh del interval reads will use 96 for the encoder type field, 97 for the kWh rec interval channel, 98 for the kVARh del interval channel, and 99 for the kVARh rec interval channel.

 

For more information reach out to your Schneider Electric Utility Account Executive, Regional Manager, or local Sales Representative.

Labels
  • Labels:
  • ION 7400
  • ION 8650
  • Utility Metering
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.