DNP and Modbus Data Scaling in ION Meters

Power Monitoring and Energy Automation NAM

This forum is created for the exchange of information and open dialogue regarding electrical power monitoring and energy automation products and services. Participants will have access to downloadable material as well as chat opportunities with subject matter experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution NEMA
  • Power Monitoring and Energy Automation NAM
  • DNP and Modbus Data Scaling in ION Meters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
7
Michael_Neas
Ensign Michael_Neas Ensign
3
Robert_Lee
Admiral Robert_Lee Admiral
2
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic T300
product field
Schneider Electric
PowerLogic ION9000
product field
PowerLogic
PowerLogic ION8650 series
field url
PowerLogic
PowerLogic ION7400 series
Load more

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Monitoring and Energy Automation NAM
Start a Topic
N4th4n13L
Lieutenant JG N4th4n13L Lieutenant JG
Lieutenant JG

Posted: ‎2022-03-01 01:37 PM

0 Likes
0
2635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-01 01:37 PM

DNP and Modbus Data Scaling in ION Meters

ION Meters support both DNP and Modbus protocols for SCADA communications, but determining the raw values isn't always straight forward. When scaling is 1 and the input values are within the bounds of the register the raw values will equal the source values of the DNP Slave Export or Modbus Slave modules.

 

How do you determine the values when the scaling is not a factor of 10, and how to validate those values. Each export module in the meter can be scaled differently and looking at the setup registers for the module will help verify the scale. In general the value/bit will be the input range/output range. The input range for DNP modules will be IONFull minus IONZero, and output range will be DNPFull minus DNPZero. The input range for Modbus modules is InFull minus InZero, and output range is OutFull minus OutZero. There may also be an offset that needs to be accounted for if the equivalent DNP value of 0 is not equal to a source value of 0.

 

An example for DNP would be a meter that is setup for frequency that is setup for IONZero equal to 58, IONFull equal to 62, DNPZero equal to -32768, and DNPFull equal to 32767. In this example frequency also has an offset of 60. The input range would be 62 - 58 which equals 4. The output range would be 32767 - -32768 which equals 65535. The Hz/bits would be 4/65535 which equals 0.000061036 Hz/bit or 16383.75 bits/Hz. If the source value is 59.98 as an example, the raw value would be (59.98-60) Hz * 16383.75 bits/Hz = -328 bits rounded. Which is the raw value we would expect in the DNP Master. This same process can be used when calculating the expected Modbus value from the meter. Register format and bounds should also be accounted for when calculating raw values. For example, if a meter has a scaling of one for primary volts phase - phase and is setup for unsigned 16bit registers. A 765kV meter would have 765,000 volts on the source input which would be above the maximum value for a 16bit unsigned register. The DNP master would only see 65,335. 

 

Calculating raw values by hand, or using a spreadsheet can be time consuming and may be susceptible to error. Using a protocol analyzer to validate data can be more reliable and efficient. Once configured can quickly validate scales and raw values to compare with SCADA during meter commissioning and installation. We can provide a similar solution as a protocol analyzer with our Easergy T300 RTU using the HU250 module. If you would like more information please reach out to your regional account executive or subject matter expert.

Labels
  • Labels:
  • Easergy T300
  • ION 7400
  • ION 8650
  • ION 9000
  • Utility Metering
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.