Posted: 2021-08-19 06:17 AM
Quantum 140CRA31200 firmware V >= 2.14
Hi community,
could someone give the .ldx file for Firmware update 140CRA31200 with (SV >=2.14), this is required for upgraded to M580 HSBY using Quantum ERIO..
Thank you
- Labels:
-
02. Modicon M580 ePAC
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-19 06:29 AM
Hi Mawan,
Kindly check the following link from se.com where you can find the latest available SV version for the 140CRA31200.
As long as SV >=2.14 it works fine with the M580 CPU, I suggest using the latest available SV 2.70 version for the 140CRA31200 module.
https://www.se.com/ww/en/product/140CRA31200/quantum-rio-drop-e-ip-1ch/
I hope this will provide help.
Best Regards
Wasif
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-19 06:29 AM
Hi Mawan,
Kindly check the following link from se.com where you can find the latest available SV version for the 140CRA31200.
As long as SV >=2.14 it works fine with the M580 CPU, I suggest using the latest available SV 2.70 version for the 140CRA31200 module.
https://www.se.com/ww/en/product/140CRA31200/quantum-rio-drop-e-ip-1ch/
I hope this will provide help.
Best Regards
Wasif
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-19 06:42 AM
Hi Wasif,
Thanks for your quick response..
Yess, the problem already solved just now the root cause is one of the ERIO still using the old firmware..
thank you in advanced