Issue
EBO server (ES/AS/Edge) Trace.log shows COV publisher errors.
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Enterprise Server
- Building Operation Automation Server
- Building Operation Edge Server - Standard
Cause
A BACnet device is misconfigured and trying to perform COV subscription that produces an error.
Resolution
- Review EBO server Trace.log
- EXAMPLE:
2023-12-28 13:54:05.124 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <analog-value, 201> failed. Status: 0x8001001f 2023-12-28 13:54:07.354 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <binary-value, 202> failed. Status: 0x8001001f 2023-12-28 13:55:05.173 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <analog-value, 201> failed. Status: 0x8001001f 2023-12-28 13:55:07.420 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <binary-value, 202> failed. Status: 0x8001001f 2023-12-28 13:56:02.921 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <analog-value, 204> failed. Status: 0x8001001f 2023-12-28 13:56:05.213 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <analog-value, 201> failed. Status: 0x8001001f 2023-12-28 13:56:07.673 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <binary-value, 202> failed. Status: 0x8001001f 2023-12-28 13:56:09.862 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <binary-value, 205> failed. Status: 0x8001001f 2023-12-28 13:57:02.932 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <analog-value, 204> failed. Status: 0x8001001f 2023-12-28 13:57:05.247 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <analog-value, 201> failed. Status: 0x8001001f 2023-12-28 13:57:07.719 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <binary-value, 202> failed. Status: 0x8001001f 2023-12-28 13:57:09.874 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <binary-value, 205> failed. Status: 0x8001001f 2023-12-28 13:58:02.945 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <analog-value, 204> failed. Status: 0x8001001f 2023-12-28 13:58:05.288 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <analog-value, 201> failed. Status: 0x8001001f 2023-12-28 13:58:07.767 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <binary-value, 202> failed. Status: 0x8001001f 2023-12-28 13:58:09.889 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <binary-value, 205> failed. Status: 0x8001001f
- EXAMPLE:
- Lookup the BACnet Error Code: Decoding BACnet Errors - Schneider Electric Community (se.com)
- EXAMPLE: 0x8001001f is unknown object, so a device is trying to subscribe to an object (Object Type + Object ID) that does not exist.
- NOTE: There could be other error codes not used in this example that are reported.
- Enable trace by navigating to ~/System/Modules/Trace/Loggers/nsp/nsp.pin/nsp.pin.BACnet/nsp.pin.BACnet.Oms/nsp.pin.BACnet.Oms.COV and change from Information to Trace.
- Wait for time to pass so Trace.log can collect more records.
- Review EBO server Trace.log to find the new line before the error, identifying the controller with the misconfiguration.
- Example: MSTP device (MAC 3) on local MSTP network is misconfigured for unconfirmed COV to BV 202
2023-12-28 14:11:08.439 [T] [2817683712] nsp.pin.BACnet.Oms.COV SubscribeCOV from local network, MAC 3 process 1: <binary-value, 202>, lifetime 18000s, unconfirmed 2023-12-28 14:11:08.441 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <binary-value, 202> failed. Status: 0x8001001f - Example: IP Device (MAC 192.168.198.136:47808) is misconfigured for confirmed COV to AV 204
2023-12-28 14:07:03.073 [T] [2817683712] nsp.pin.BACnet.Oms.COV SubscribeCOV from local network, MAC 192.168.198.136:47808 process 1: <analog-value, 204>, lifetime 18000s, confirmed 2023-12-28 14:07:03.075 [E] [2817683712] nsp.pin.BACnet.Oms.COV COVPublisher: Subscribing to <analog-value, 204> failed. Status: 0x8001001f
- Example: MSTP device (MAC 3) on local MSTP network is misconfigured for unconfirmed COV to BV 202
- Disable trace by navigating to ~/System/Modules/Trace/Loggers/nsp/nsp.pin/nsp.pin.BACnet/nsp.pin.BACnet.Oms/nsp.pin.BACnet.Oms.COV and change from Trace to Information.
- Inspect the listed BACnet devices and correct the misconfiguration.