Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84798members
354250posts

Quantum 140CRA31200 firmware V >= 2.14

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Solved
Mawan
Crewman Crewman
Crewman
0 Likes
2
525

Quantum 140CRA31200 firmware V >= 2.14

Hi community,

 

could someone give the .ldx file for Firmware update 140CRA31200 with (SV >=2.14), this is required for upgraded to M580 HSBY using Quantum ERIO..

 

Thank you  

Tags (1)

Accepted Solutions
Siddiqui
Ensign Ensign
Ensign

Re: Quantum 140CRA31200 firmware V >= 2.14

Hi Mawan,

 

Kindly check the following link from se.com where you can find the latest available SV version for the 140CRA31200.

As long as SV >=2.14 it works fine with the M580 CPU, I suggest using the latest available SV 2.70 version for the 140CRA31200 module.

 

https://www.se.com/ww/en/product/140CRA31200/quantum-rio-drop-e-ip-1ch/

 

I hope this will provide help.

 

Best Regards

Wasif

See Answer In Context

Attachments
Tags (1)
2 Replies 2
Siddiqui
Ensign Ensign
Ensign

Re: Quantum 140CRA31200 firmware V >= 2.14

Hi Mawan,

 

Kindly check the following link from se.com where you can find the latest available SV version for the 140CRA31200.

As long as SV >=2.14 it works fine with the M580 CPU, I suggest using the latest available SV 2.70 version for the 140CRA31200 module.

 

https://www.se.com/ww/en/product/140CRA31200/quantum-rio-drop-e-ip-1ch/

 

I hope this will provide help.

 

Best Regards

Wasif

Attachments
Tags (1)
Mawan
Crewman Crewman
Crewman

Re: Quantum 140CRA31200 firmware V >= 2.14

Hi Wasif,

 

Thanks for your quick response..

 

Yess, the problem already solved just now the root cause is one of the ERIO still using the old firmware..

 