Quantum Modernization to M580

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Quantum Modernization to M580
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
6
ciupol
Lieutenant ciupol
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Solved
Rifqi_Imanto
Lieutenant JG Rifqi_Imanto Lieutenant JG
Lieutenant JG

Posted: ‎2020-03-29 10:32 PM

0 Likes
4
6077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-03-29 10:32 PM

Quantum Modernization to M580

Hi,

 

is it possible to to replace Quantum 140 CPU 43412U to M580 BME P58 1020 ? with all module replaced, and with minimal risk and modification.

 

image.png

 

and what possibility issue will appear? 

  1. State Ram Addressing (Quantum Start from 1, and M580 start from 0) will make some Real/Float type data error. and how to fix it?
  2. Re-Addressing on SCADA (Citect SCADA) side? (User doesn't want to do this)
  3. anything else?

 

Thanks

@Anonymous user 

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2020-03-29 11:57 PM

3 Likes
2
6074
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-03-29 11:57 PM

Hi,

1 & 2. Re-adressing is not needed when  %SW138 - %SW141 are set with an initial value of 1. These Status words are available for M580 and give the STATE-RAM addresses an offset (of 1), making all STATERAM addresses identical as in your Quantum application. No need to change your SCADA application for this.

Unity M580 Application Converter (UMAC) is the tool for conversion of Quantum/Premium to M580 and will set these values automatically.

 

Also UMAC will add some code to make 32-bit variables (float, DINT), compatible with M580, without impacting your SCAD application.

 

3. Check connections on the CPU. 140CPU43412 has 2 Modbus ports and MB+, they do not show on this bitmap, but devices might be connected. For Modbus connection add a BMXNOM0200 (Check cables) and for MB+ add a MB+ Proxy module.

 

Conversion cabling for the IO modules is available, making the IO conversion more easy.

R.Roozee
Sr Solution Architect (SAE Master)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2020-03-29 11:57 PM

3 Likes
2
6075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-03-29 11:57 PM

Hi,

1 & 2. Re-adressing is not needed when  %SW138 - %SW141 are set with an initial value of 1. These Status words are available for M580 and give the STATE-RAM addresses an offset (of 1), making all STATERAM addresses identical as in your Quantum application. No need to change your SCADA application for this.

Unity M580 Application Converter (UMAC) is the tool for conversion of Quantum/Premium to M580 and will set these values automatically.

 

Also UMAC will add some code to make 32-bit variables (float, DINT), compatible with M580, without impacting your SCAD application.

 

3. Check connections on the CPU. 140CPU43412 has 2 Modbus ports and MB+, they do not show on this bitmap, but devices might be connected. For Modbus connection add a BMXNOM0200 (Check cables) and for MB+ add a MB+ Proxy module.

 

Conversion cabling for the IO modules is available, making the IO conversion more easy.

R.Roozee
Sr Solution Architect (SAE Master)
Reply

Link copied. Please paste this link to share this article on your social media post.

Rifqi_Imanto
Lieutenant JG Rifqi_Imanto Lieutenant JG
Lieutenant JG

Posted: ‎2020-03-30 12:35 AM

In response to RoozeeR
1 Like
0
6072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-03-30 12:35 AM

@RoozeeR 

 

ok nice..

for point 3. there is only IO, no communication bus to field. 

 

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-09-29 06:25 AM

0 Likes
0
6027
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-29 06:25 AM

Hello 

 

You need to have minimum the Level 4 M580 - BMEP584040 to support Quantum migration and integrate M580 rack with existing Quantum IO.

 

Also, Schneider has an internal tool to migrate existing Quantum program to M580 program without having to mess PLC addressing offsets and keeping SCADA addressing intact.  Please discuss with your local SE sales person 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Archie.Levivi22
Archie.Levivi22
Cadet

Posted: ‎2024-10-23 06:33 AM

In response to RoozeeR
0 Likes
0
1334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 06:33 AM

Hi 

 

Do you have a part number for this "Conversion cabling for the IO modules is available, making the IO conversion more easy." Cable?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of