Hi All,
i want to ask about how to read and describe this data
i want to want to draw phasor diagram from this data
how to read it and how to describe it into phasor diagram ?
Link copied. Please paste this link to share this article on your social media post.
A rough approximation of phasor diagram
Looks like CT1 and CT2 are switched.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Arsyad_Azhari ,
You can think of this number as the angle between Voltage and current. Lets assume Va at 0 Vb 120 and Vc 240, then current A could be at 89 degrees, Current B, 321 degrees, current C, 197 degrees.
This is just an example.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
first question :
this angle number is positive so it is counterclockwise isn't it ? or else ?
second question :
current B = 321 degrees, is it counted from Va (0 degrees) or from Vb ?
and also for currrent C = 197 degrees, is it from Va (0 degrees) or from Vc ?
Link copied. Please paste this link to share this article on your social media post.
Hello @Arsyad_Azhari ,
I do not know the specifics of the PM5000 series. @Ramasamy_N would you be able to answer the questions regarding PM5300 and phase angle screens and how to create phasor diagram.
Thank you,
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @Arsyad_Azhari
We can create the phasor diagram if we have the voltage angles V1 to V2 and V2 to V3 and V3 to V1 or we can calculate the angles under assumption of 120 degrees each. like V1=0, V2=120 and V3=240.
Yes, the phase angle number is positive and counterclockwise.
The angle V2- A2 = 201 degrees, is it counted from V2 (120 degrees) and current V3-A3 = 317 degrees, is it counted from V3 (240 degrees).
Can you check the physical connection of I2 and I3 CT inputs? It seems to be interchanged.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
A rough approximation of phasor diagram
Looks like CT1 and CT2 are switched.
Regards,
Charles