is A9MEM1573 bi-directional measurement

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • is A9MEM1573 bi-directional measurement
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
516
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
125
Ramasamy_N
Captain Ramasamy_N Captain
115
Robert_Lee
Admiral Robert_Lee Admiral
96
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Grant_IPACS
Commander Grant_IPACS
Commander

Posted: β€Ž2023-05-25 08:59 PM

0 Likes
5
1578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2023-05-25 08:59 PM

is A9MEM1573 bi-directional measurement

Hi we have a customer looking to add a battery system to their system, the switchboard already has existing powertags & PAS, which is makes things easy, but i am concerned energy measured is not bi-directional.

 

ie the battery system will charge & discharge at different times of the day, can we separate the two into distinct measurements to confirm the systems performance?

 

 

Regards

Grant
Labels
  • Labels:
  • PowerTag Energy
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: β€Ž2023-05-26 01:54 AM

1 Like
1
1566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2023-05-26 01:54 AM

hi @Grant_IPACS 

 

Can you please
1) update your panel server to last firmware1.6 to be sure that the PowerTag is managed as a bidirectional meter then verify if it solve your issue in the real time measurement web page (red rectangle in screenshot hereunder)

(links to download firmware and doc available in SE community Gateway and energy server post

https://community.se.com/t5/Gateways-and-Energy-Servers/EcoStruxure-Panel-Server-Our-new-Generation-... 

 

 

2) If it does not solve your issue, can you please share the firmware version of the PowerTag available in Panel server web Page (available in red circle in screenshot hereunder)

 

 

Thierry_Baudard_0-1685091156854.png

 

Best regards

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions

See Answer In Context

Reply
Replies 5
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: β€Ž2023-05-26 01:54 AM

1 Like
1
1567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2023-05-26 01:54 AM

hi @Grant_IPACS 

 

Can you please
1) update your panel server to last firmware1.6 to be sure that the PowerTag is managed as a bidirectional meter then verify if it solve your issue in the real time measurement web page (red rectangle in screenshot hereunder)

(links to download firmware and doc available in SE community Gateway and energy server post

https://community.se.com/t5/Gateways-and-Energy-Servers/EcoStruxure-Panel-Server-Our-new-Generation-... 

 

 

2) If it does not solve your issue, can you please share the firmware version of the PowerTag available in Panel server web Page (available in red circle in screenshot hereunder)

 

 

Thierry_Baudard_0-1685091156854.png

 

Best regards

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply
Grant_IPACS
Commander Grant_IPACS
Commander

Posted: β€Ž2023-05-26 08:24 PM

0 Likes
0
1556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2023-05-26 08:24 PM

Hi @Thierry_Baudard , apologies, this was more of a capability question (as we have not purchased the unit yet), but from your post the answer it is capable.

 

 

Regards

Grant
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: β€Ž2023-05-28 11:21 PM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2023-05-28 11:21 PM

@Grant_IPACS , @kanyeshirt34 

 

No worries, you are welcome for question πŸ™‚

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply
Horacio1
Lieutenant JG Horacio1 Lieutenant JG
Lieutenant JG

Posted: β€Ž2023-06-06 03:24 PM

0 Likes
0
1483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2023-06-06 03:24 PM

@Thierry_Baudard so this means that even a really simple device such as a powertag is a bidirectional meter or sometimes called two-way meter???

 

Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: β€Ž2023-06-07 02:59 AM

0 Likes
0
1474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2023-06-07 02:59 AM

@Horacio1 

 

Yes absolutely , as you mention, PowerTag is a two way meter β€Œβ€ŒπŸ˜Š

 

Best regards

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore