Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
HI,
Our partners see the IEM2000 delivered to them as 50Hz and want to return because we are using 60Hz as system frequency.
I see the technical data sheet that iEM2155 is 50Hz and 60Hz,
also I see the datasheet that it reads from 45Hz to 65Hz range.
Do our iEM2155 is an autodetect for frequency?
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa427078_brid
iEM2155 meter does not suitable for 60Hz frequency network.
You can suggest to replace with iEM2050 for 60Hz application.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa427078_brid
iEM2155 meter does not suitable for 60Hz frequency network.
You can suggest to replace with iEM2050 for 60Hz application.
Regards,
Ramasamy N