Hello community,
A customer needs to start up two AccuSine PCS+ that have been in storage for three years, so I have the following question:
Do I have to do a reforming (similar to VFD) of the DC capacitors? and if so, is there any documentation?
Regards
Link copied. Please paste this link to share this article on your social media post.
Hello Alank
Please refer the attached document, which is applicable for PCSP Accusine models too. Hope this clarify's your doubts.
If you still had any queries, feel free to get back to us.
Regards
Arunprasad
Link copied. Please paste this link to share this article on your social media post.
Hello Alank
Please refer the attached document, which is applicable for PCSP Accusine models too. Hope this clarify's your doubts.
If you still had any queries, feel free to get back to us.
Regards
Arunprasad