iEM 3255 Digital Input
Dear Sir's
I want to count pulses from a sensor with the iEM3255 Digital Input available in this meter.
I would like to know how many pulses can I count every second?
I check everywhere but I don´t find this information!
If someone can give me this information I will appreciate,
Thanks very much,
Best Regards,
Luís Dias
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Luis,
The following infomation was found on the PM3200 series user manual.
Best luck to you,
Niara

Posted: 2015-11-19 06:00 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Luis,
iEM3000 has 4 DI functions of Digital Input:input status,input metering,tariff control and partial reset. For your application, you need to set the DI function to "input metering": the meter counts and records the number of incoming pulses. And you must also configure "In.Pulse constant",to indicate how many units each incoming pulse represents. More information please refer to the user manual: http://www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/239000/FA239...
Hope it helps
Leo

Posted: 2020-01-09 04:00 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi.
We need to know how we can visualize this register. A mean, we can read it via MODBUS, but isn't clear if we can see it on the display. Can be this possible??