Dear Members, we apologize for any disruption or inconvenience caused by the recent spam incidents, and we want to assure you that our dedicated team is actively investigating each reported instance of spam and implementing robust measures to mitigate the impact. Learn more on Spams Mitigation Guidelines
Thank you,
Schneider Electric Community Team
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
We are discussing with Cummins, for Energy Monitoring in Sync Panel...Application calls for KW & KWH input to Sync PLC and at the same time they need to give all parameters to Clients EMS or BMS. So for this can they use Analog Output from Meter for KW & KWH as input to PLC and RS485 or Ethernet connectivity from Meter to Client.
We have PM8M2222 with PM800....can it be used for above application ?
What alternate we can offer for above in PM5000 ?
Regards,
Chetan Dhake.
Link copied. Please paste this link to share this article on your social media post.
Hi chetan,
Yes you cab use the analog output from the
PM8M2222 to sync PLC , one register should be linked to one digital output.For PM5000, i am now in the train, i will look for a solution this evening!
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Sorry i meant analog output, and don' t forget max and min value. Your PLC should have an analog input 4-20ma
Link copied. Please paste this link to share this article on your social media post.
Not possible with PM5xxx - must wait for PM8000 I believe.
Link copied. Please paste this link to share this article on your social media post.
Hi,
It is not possible with PM5000 at the moment!
Link copied. Please paste this link to share this article on your social media post.
Would you update this thread as "answered", if you are satisfied with the reply?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
kWh and kVARh are accumulated value they keep increase you cannot use the analog output 2-40 mA, instead the digital output must be use to send energy pulses to the PLC counter.