What includes the BCPMSCA60S reference
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2017-09-1410:44 AM
Models with more than 2 as the number of circuits include 50 A branch CTs with 2 meter leads and 1.8M round ribbon cables.
The BCPMSC models with 1, 2 or Y63 as the number of circuits DO NOT INCLUDE ANY branch CTs or ribbon cables (they include only the Main board and adapater board assemblies) . These models are provided to allow users to order a
specific combination of CT quantities, CT sizes, CT lead lengths and ribbon cable styles and lengths.
The CTs and cables must be ordered separately.
The PowerLogic BCPMSC uses .333 V AC output split-core CTs for the auxiliary inputs. These CTs are ordered separately from the BCPM.
Link copied. Please paste this link to share this article on your social media post.
2017-09-1410:44 AM
Models with more than 2 as the number of circuits include 50 A branch CTs with 2 meter leads and 1.8M round ribbon cables.
The BCPMSC models with 1, 2 or Y63 as the number of circuits DO NOT INCLUDE ANY branch CTs or ribbon cables (they include only the Main board and adapater board assemblies) . These models are provided to allow users to order a
specific combination of CT quantities, CT sizes, CT lead lengths and ribbon cable styles and lengths.
The CTs and cables must be ordered separately.
The PowerLogic BCPMSC uses .333 V AC output split-core CTs for the auxiliary inputs. These CTs are ordered separately from the BCPM.