Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

What PM800 resets are available in ION Setup 3.0

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • What PM800 resets are available in ION Setup 3.0
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
sesa71269_bridg
sesa71269_bridg Explorer
Explorer

Posted: ‎2015-12-07 11:48 AM

0 Likes
5
2055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-07 11:48 AM

What PM800 resets are available in ION Setup 3.0

Dear Colleagues,

In the Schneider FAQ in the

What PM800 resets are available in ION Setup 3.0

topic the method is written to add new reset functions to ION 3 setup.

Based on this I would like to expand ION 3.0 menu for PM8000 with the following points:

- enable EN50160 evaluation
- reset EN50160 evaluation results

- acknowledge and reset active alarms log

- acknowledge and reset historcal alarms log

May I ask anybody to help me on this. How to do this?

Thanks, Laszlo

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Bojan
Bojan Leader
Leader

Posted: ‎2015-12-07 12:59 PM

0 Likes
4
2005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-07 12:59 PM

Hi Laszlo,

I think Robert Lee would be the best person to ask for the help,

Best Regards,

Bojan

Reply
Yut
Yut
Leader

Posted: ‎2015-12-07 08:41 PM

1 Like
2
2005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-07 08:41 PM

try to go to C:\Program Files\Schneider Electric\ION Setup\Tables\PM8000\Version 2.0 Default (depends on what version you want)

edit RealTime.pml with notepad add last line on page2 bye imitate the reset control

for enable or disable use Enables.pml then do the same thing.

You must know the handles (in Hexadecimal) of the external pulse and external Boolean to be use.

Reply
sesa71269_bridg
sesa71269_bridg Explorer
Explorer

Posted: ‎2015-12-07 11:30 PM

0 Likes
0
2005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-07 11:30 PM

thanks Bojan

Reply
sesa71269_bridg
sesa71269_bridg Explorer
Explorer

Posted: ‎2015-12-07 11:30 PM

0 Likes
0
2005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-07 11:30 PM

thanks Yut, let us try as you described !

Reply
sesa71269_bridg
sesa71269_bridg Explorer
Explorer

Posted: ‎2015-12-08 05:41 AM

0 Likes
0
2005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-08 05:41 AM

Yut, you said: "You must know the handles (in Hexadecimal) of the external pulse and external Boolean to be use."

How and from where?

Anyway I made a mistake this is needed for PM8000 (and not PM800) for my SI partner. Is it the same process for PM8000?

Sorry for inconvenience ...

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore