2015-05-2007:24 AM
Voltage Coupler
Hi people,
We have an application in Brazil that use an voltage of 1500Vdc for Solar Plant and our product (HV1700) is limited in a 1000Vdc. Anybody knows if is possible to use a voltage coupler of the Bender (AGH150W-4)?
Link copied. Please paste this link to share this article on your social media post.
2015-05-2204:35 AM
Hi,
Voltage adaptors are designed to work with their associated IMDs, and it is not possible to mix the products. For instance, voltage adaptor IM400-1700 works with IM400, only. Be informed that we are working at having such adaptor up to 1500VDC by the end of 2015.