VigilOhm IFL12 can't communicate in PME 10.0!

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • VigilOhm IFL12 can't communicate in PME 10.0!
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Kelvin2805
Crewman Kelvin2805
Crewman

Posted: ‎2022-07-23 10:45 PM . Last Modified: ‎2022-07-24 07:20 AM

0 Likes
4
1415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-23 10:45 PM

VigilOhm IFL12 can't communicate in PME 10.0!

When I add IM400 and IFL12 devices in PME system, IM400 is good connect with PME, but IFL12 some time connect good but almost time is time out status. Please kindly help me to solve this problem.

See reference picture

@Charles_Murison  : Help me for this case. Any things else can direct discuss via Whatapps (+84)934001505

Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Kelvin2805
Crewman Kelvin2805
Crewman

Posted: ‎2022-07-25 01:30 AM

0 Likes
0
1388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-25 01:30 AM

Any body can help me for this urgent case? Hope to received your instructs soon.

@Charles_Murison @sbeadle 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-07-25 08:27 AM

0 Likes
2
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-25 08:27 AM

Hello @Kelvin2805 .

 

If you require urgent support you should be contacting your location Customer care Team technical support. (Se.com -> Support -> contact technical support). Also note that this question was not asked in the PME forum, chances are most users of PME will never see this question.

I do not know the IFL12 device so I cannot speak to that product. In General, if you have multiple devices on a gateway, your timeout settings in software needs to be at least (# devices * gateway timeout settings). Lets take for example a system with 5 devices and a gateway timeout of 3 seconds, 4 of these devices are not responding, why is not important. Assume that PME is asking for data from all five devices but only the last one will respond, PME will start all 5 requests, then send a request to first device via gateway, gateway will wait 3 seconds, before sending response back. Then PME will send request for second device, wait 3 seconds, get a response back, At this point it has been 6 seconds since PME first started the request for data from the second device. Expand this to all five devices and PME will have waited ~12 seconds before the fifth device even has a chance to respond.

 

I cannot say for certain that this is the cause but could be a factory, a few devices not responding on a serial loop can take up most of the bandwidth of the loop and never get any data. One test could be to disable most of the devices in the serial loop that are timing out and see if the remaining ones come back.

 

Further troubleshooting will require tech support case.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Kelvin2805
Crewman Kelvin2805
Crewman

Posted: ‎2022-07-25 09:48 AM

0 Likes
1
1357
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-25 09:48 AM

Dear @Charles_Murison 

I tried to disable almost of device except one device VigilOhm IFL12MCT in serial loop but the result still time out status.

I also change the time out setting of devices and gateway, but it not change anything.

Until now, I don't known what is the exactly reason of this issue. I also take a requestion to customer care support from Schneider, but still not get the solutions.

Hope to get any ideas from communities to solve. ðŸ˜ª

Attachments
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-07-25 10:20 AM . Last Modified: ‎2022-07-25 10:20 AM

0 Likes
0
1349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-25 10:20 AM

Hello @Kelvin2805 ,

 

You could try testing communications outside of PME. If you use a modbus client test application like tester.exe (KB), modscan, modbus poll etc, do you see the same response as PME. If you do get the same response as PME. it could be issue is outside PME altogether.

Tech support will be your best option moving forward.

 

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of