VT wiring connections for ION 9000.

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • VT wiring connections for ION 9000.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Miyai
Lieutenant Miyai
Lieutenant

Posted: ‎2022-10-18 09:09 PM

0 Likes
2
1896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-18 09:09 PM

VT wiring connections for ION 9000.

Hello, 

 

Please advise on VT wiring connections for ION 9000.

 

Customer wants to record V0 waveforms.

Are the following wiring connections correct?

Also, should VN and VE be connected?

 

 

 

 

ION9000.jpg

 

 

I have already explained to the customer that the V0 accuracy range is 57-400V.

 

 

Best regards,

Miyai

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2022-10-31 05:01 PM

2 Likes
1
1759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-31 05:01 PM

That wiring and the term "V0" appear to correspond to the zero-sequence voltage.

With the usual definition of zero-sequence voltage, the 2nd set of PTs would require a ratio (either real or programmed in the meter) of 1/3 of the primary set.

 

Assuming the 6 PT's are all the same, it's trivial to simply configure the V4 PT ratio to be 1/3rd of the other ratio.

 

For wiring, I recommend ensuring the meter's VN connection be wired to the ground point shared for both sets of PT secondary's, everything else looks fine.

 

For configurations with PTs, the VE terminal will be unused, but we recommend you connect to ground anyway (usually the same place as the PT secondary grounding)

 

The voltage accuracy for the ION9000 under very low signal levels (voltage dips) is governed by the IEC61000-4-30 Class A specification:

+/-0.2% of Udin (aka. 0.2% of nominal secondary voltage)

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
DanL
Captain DanL Captain
Captain

Posted: ‎2022-10-31 05:01 PM

2 Likes
1
1760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-31 05:01 PM

That wiring and the term "V0" appear to correspond to the zero-sequence voltage.

With the usual definition of zero-sequence voltage, the 2nd set of PTs would require a ratio (either real or programmed in the meter) of 1/3 of the primary set.

 

Assuming the 6 PT's are all the same, it's trivial to simply configure the V4 PT ratio to be 1/3rd of the other ratio.

 

For wiring, I recommend ensuring the meter's VN connection be wired to the ground point shared for both sets of PT secondary's, everything else looks fine.

 

For configurations with PTs, the VE terminal will be unused, but we recommend you connect to ground anyway (usually the same place as the PT secondary grounding)

 

The voltage accuracy for the ION9000 under very low signal levels (voltage dips) is governed by the IEC61000-4-30 Class A specification:

+/-0.2% of Udin (aka. 0.2% of nominal secondary voltage)

Tags (1)
  • Tags:
  • english
Reply
Miyai
Lieutenant Miyai
Lieutenant

Posted: ‎2022-11-06 09:02 PM

0 Likes
0
1698
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-06 09:02 PM

Hi @DanL 

 

Thank you for advice.

We asked the customer to consider the ground.

 

 

 

Regards,

Miyai

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of