Hallo Everyone
1. Which values are reset when a Peak Demand Reset is done?
2. If Energy Delivered isn't part of the values above, how can we rest the Energy Delivered value?
Regards
Tobie
  • PM8000
Charles_Murison
Posted: ‎2022-11-01 09:29 AM
1
2060
Hello @Anonymous user ,
Demand = kw, energy = kwh. resetting demand does not reset energy. Different modules in the meter. The image below shows the values reset when peak demand reset is triggered.
Energy Delivered can be reset in 2 ways, First is to trigger the master reset (does not reset communication or configuration settings). The second option is to use ION Setup and go to setup assistant -> Template -> Register Edit -> energy -> Edit, then enter in 0 for kWh Del and possibly other energy values if desired.
Charles
Charles_Murison
1
2061
Charles
Posted: ‎2022-11-09 01:24 AM
Thank you @Charles_Murison