Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84704members
354083posts

Using ION7550RTU as a remote display for PM820

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

kaito_hokama_ry
Crewman
Crewman
0 Likes
4
392

Using ION7550RTU as a remote display for PM820

Does someone know how to configure ION7550-RTU as a remote display for PM820?

ION7550RTU: S7550B0N9B9A0A0A

Connection: RS-485

4 Replies 4
Yut
Captain
Captain

Re: Using ION7550RTU as a remote display for PM820

1. Modbus Import module or

2. Modbus Master Device module together with Modbus Master Map module

Then link output to Display module or do data logging or both.

Please see ION Reference

kaito_hokama_ry
Crewman
Crewman
0 Likes
2
330

Re: Using ION7550RTU as a remote display for PM820

I setup Comm Module, Modbus Master Device Module and Modbus Master Map Module.

Then linked to Display Module but I still can't get date from PM820.

On Modbus Master Map Module, I put a data as "LbVln a,SR41120,FUINT16,NR1,S0.1,O0,".

Someone knows what the issue is?

ION7550RTU-Comm.JPG

ION7550RTU-MMD.JPG

ION7550RTU-MMM.JPG

Yu_Diao
Commander Commander
Commander

Re: Using ION7550RTU as a remote display for PM820

In Desginer, hold down "Shift" and click Modbus Master Device module's output, do you see any values in the output regsiters? If not, check the "Modbus Master Option" module to assign the correct com port to "Serial Connection 1".

kaito_hokama_ry
Crewman
Crewman
0 Likes
0
330

Re: Using ION7550RTU as a remote display for PM820

Thank you.

I will check that first.