Unusual Voltage Measurements with ION9000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Unusual Voltage Measurements with ION9000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All
Related Products
product field
Schneider Electric
PowerLogic ION9000

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
JoseCarlosUP
JoseCarlosUP
Cadet

Posted: ‎2023-10-16 02:56 PM

0 Likes
1
1025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-16 02:56 PM

Unusual Voltage Measurements with ION9000

Hello,

We are currently facing an unusual situation with our ION9000 meter. The equipment is being used for voltage measurement in the 11.8kV (3-phase delta) PCC using a PT-CT set as per the diagram in the image. The instrument voltage mode is configured for 3W-WYE. Yes, we are aware that this is not the appropriate voltage mode for the wiring diagram. However, the strange aspect is that, with the mentioned configuration, the voltage measurements only show a 4% voltage imbalance on phase A (L1) and exhibit high stability.

To delve further into this issue, we have removed the ION for laboratory testing. During the testing with a low-voltage grid (without PT) using the same wiring diagram (noting that VN is not connected), we observed unbalanced voltages These were considerably worse than the field measurement, with all phases displaying pronounced oscillations. Even more peculiar is the that with another meter in the PCC (configured according to the wiring diagram), voltage measurements show no unbalance. It appears that the PT-CT set is functioning correctly.

Do you have any insights into what might be causing this slight unbalanced voltage measurement with the ION?

Best regards.

  • Thumbnail of PowerLogic ION9000
    Schneider Electric
    PowerLogic ION9000
View products (1)
Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-10-02 11:06 AM . Last Modified: ‎2024-11-29 08:41 AM

1 Like
0
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-02 11:06 AM

Hello @JoseCarlosUP ,

 

3W-wye is very much not the correct volts mode to use. The 3W-wye has a very, very specific use case and will not work with the configuration you are using. Is there a reason why customer does not want to connect VN to VE? 

 

While the meter can be 4W-wye volts mode, many features can still be configured to use the VLL values. To use 4W-wye, the VN connection will need to be connected.

With Meter in 3W-wye mode, the meter is measuring V1 to VN where VN is floating. I am not surprised that using a floating reference could cause strange readings.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Reply 1
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-10-02 11:06 AM . Last Modified: ‎2024-11-29 08:41 AM

1 Like
0
687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-02 11:06 AM

Hello @JoseCarlosUP ,

 

3W-wye is very much not the correct volts mode to use. The 3W-wye has a very, very specific use case and will not work with the configuration you are using. Is there a reason why customer does not want to connect VN to VE? 

 

While the meter can be 4W-wye volts mode, many features can still be configured to use the VLL values. To use 4W-wye, the VN connection will need to be connected.

With Meter in 3W-wye mode, the meter is measuring V1 to VN where VN is floating. I am not surprised that using a floating reference could cause strange readings.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of