Dear All,
I apologize if I post this question in the wrong place.
I have a monitor PM5110. I would like to install a simple combined alarm indicator lamp remotely, which would be triggered if one of preset alarms comes ON.
How can I do it?
I understand that this monitor has DO, which can be used only for energy consumption monitoring.
There is also Modbus.
Please, suggest the right approach.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hi @ddm,
The PM5100 series does not allow digital output for alarm configuration. It only has one digital output, which can only be configured for pulsing energy.
Link copied. Please paste this link to share this article on your social media post.
Hello @Jesus_Diaz ,
Any suggestions on how to control DO on PM5110 from alarm condition?
regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @ddm,
The PM5100 series does not allow digital output for alarm configuration. It only has one digital output, which can only be configured for pulsing energy.