Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Unable to capture rs485 readings on lora module attached to E6436H

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Unable to capture rs485 readings on lora module attached to E6436H
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
environics
environics
Explorer

Posted: ‎2025-02-17 08:07 PM

0 Likes
3
1198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-17 08:07 PM

Unable to capture rs485 readings on lora module attached to E6436H

Hello Experts,

We are trying to integrate our lora iot module to conserve E6436H meter. We captured the register values on the modscan software and accordingly modified our firmware on the lora module. We are using all the parameters as mentioned in the rs485 document with same data type, data value etc. However we are not getting any value on our lora module and we are not sure how to debug. For example on modscan register value 42700 is for total active power. On modscan we see non zero value but same register on our lora module we are getting zero value. So not sure where what's going wrong. Appreciate help.. Thanks

Labels
  • Labels:
  • ION Setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-02-20 10:54 AM

0 Likes
0
1142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-20 10:54 AM

Hello @environics ,
I am not knowable on your lora module. I can just offer basic troubleshooting suggestions. The first suggestion I can offer is to capture and analyze the RS-485 traffic. This may be easier said than done. There are tools out there that can help, for example the product at https://www.iftools.com/analyzer/index.en.php . The challenge is understanding if the lora module or E6436H is the device that is not behaving as expected.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-02-18 09:47 AM

0 Likes
2
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-18 09:47 AM

Hello @environics ,

In modbus there are address and registers that use index 1 and index 0. Depending on what your module is expecting you may have an "off by one". Modscan for example when you enter in address holding register 2700, the request on the serial line is for register 2699. Perhaps your module is using the 0 index?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
environics
environics
Explorer

Posted: ‎2025-02-19 09:09 PM

0 Likes
1
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-19 09:09 PM

Hello Charles,

I checked with our tech guys and they said they have already tried this and also different data types etc.. Still we are not getting data on our lora module.

Rgds,

Murali

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-02-20 10:54 AM

0 Likes
0
1142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-20 10:54 AM

Hello @environics ,
I am not knowable on your lora module. I can just offer basic troubleshooting suggestions. The first suggestion I can offer is to capture and analyze the RS-485 traffic. This may be easier said than done. There are tools out there that can help, for example the product at https://www.iftools.com/analyzer/index.en.php . The challenge is understanding if the lora module or E6436H is the device that is not behaving as expected.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore