Team,
What is the max number of simultaneous TCP connections a:
- PM8xxx can support?
- PM5xxx ?
- PM8xx ?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Ivan - from the PM8000 specification - 32 concurrent TCP/IP connections. Still looking into PM5000 since it is not captured in the spec..
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
To be more specific, the 32 concurrent TCP/IP connections are dedicated to Modbus TCP (port 502), but a number of additional connections are also supported.
Here is a screenshot of a good summary from the PM8000 user manual:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
What is the difference between Modbus TCP and Modbus TCP (dedicated)?
Link copied. Please paste this link to share this article on your social media post.
Thank you Usha,
Are there any documents available tgat contain this onformation that I can share with customer? Specs doc, design guides, etc?
Link copied. Please paste this link to share this article on your social media post.
The PM8000 has 8 Ethernet connections that can be shared (used by) either ION, DNP or Modbus TCP or combination of all three.
There are also 32 Ethernet connections that can only be used by Modbus TCP.
So there are 32 dedicated (can only be used by) Modbus TCP connections, and there are up to 8 additional connections which could use Modbus TCP if desired (and you didn't want any ION or DNP connections).
I've heard some people call the 8 shared connections "generic" connections as they can be used for either of the three protocols.
Modbus TCP is the only protocol that has both dedicated and shared connections, so they are differentiated in the table. The other protocols have dedicated connections (like IEC 61850).
Hope this helps.
Alana