New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Some Questions about DDD analysis
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2018-02-0106:45 AM
Some Questions about DDD analysis
I have some questions about DDD analysis on ION7650 and ION8650 (A, B) meters:
1. I know it works fine for Sag/Swells but ¿what about transients and flicker events? it will work?.
2. I have read about perturbance direction detection. (I,V) analysis for sag swells and (freq) analysis for transients, but I want to know if there is some notes or info related on how this technology is implemented on ION meters. This is important for us in order to argue the customers about his PQ issues using DDD analisys as a conclusion.
Link copied. Please paste this link to share this article on your social media post.
2018-02-2702:26 PM
The Disturbance Direction Detection (DDD) ION module has 7 trigger inputs. The module assumes that the first 4 are from the SAG module. The transient trigger inputs are optional.
Although transient events can trigger the DDD module to operate and analyse the voltage, current and power waveforms for direction scores, in my experience most sub-cycle fault events are not simply resistive and will result in low confidence DDD scores (ie. indeterminate).
Although it might be possible to trigger DDD from an RVC event, that was not the design nor tested.