Some Questions about DDD analysis

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

sesa453448_brid
Ensign Ensign
Ensign
0 Likes
2
286

Some Questions about DDD analysis

I have some questions about DDD analysis on ION7650 and ION8650 (A, B) meters:

1. I know it works fine for Sag/Swells but ¿what about transients and flicker events? it will work?.

2. I have read about perturbance direction detection. (I,V) analysis for sag swells and (freq) analysis for transients, but I want to know if there is some notes or info related on how this technology is implemented on ION meters. This is important for us in order to argue the customers about his PQ issues using DDD analisys as a conclusion.

Thanks in advance,

Regargs,

JULIO CESAR GONZALES ADVINCULA​, Carlos Eduardo RODRIGUEZ

2 Replies 2
Tom_Stevenson
Picard Picard
Picard
0 Likes
0
237

Re: Some Questions about DDD analysis

DanL
Commander Commander
Commander

Re: Some Questions about DDD analysis

The Disturbance Direction Detection (DDD) ION module has 7 trigger inputs. The module assumes that the first 4 are from the SAG module. The transient trigger inputs are optional.

Although transient events can trigger the DDD module to operate and analyse the voltage, current and power waveforms for direction scores, in my experience most sub-cycle fault events are not simply resistive and will result in low confidence DDD scores (ie. indeterminate).

Although it might be possible to trigger DDD from an RVC event, that was not the design nor tested.