Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Schneider Split core current transformers

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Schneider Split core current transformers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
AndersDahlskog
AndersDahlskog Contributor
Contributor

Posted: ‎2025-07-08 01:40 AM

0 Likes
6
2342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-08 01:40 AM

Schneider Split core current transformers

Hi

In datasheet PowerLogic™ Current Transformers (CT) Technical Datasheet | Schneider Electric

page 4 is an application example based on 2,5mm2 cable (very common to use). In our split core models on on page 14 METSECT5Hxxxxxx it seems to be a fixed soft cable with 1,5mm2 area.

Then calculating as in the application example and the requirements is 2,5mm2 can this existing 1,5mm2 used to shorting block and then switch to 2,5mm2.

How to think, calculate and use our split core CT,s with this existing cable ?

In this case the CT s is to be used with PowerLogic PM5110

 

BR/Anders

PAE EcoStruxure Power, Sweden

Attachments
Example of split core CT.docx
Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-07-11 09:27 AM . Last Modified: ‎2025-07-11 09:28 AM

0 Likes
0
2284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-11 09:27 AM

Hello @AndersDahlskog 
Lets assume that you have METSECT5HA025 CT. The maximum burden that this CT can support is 1VA, the Meter has burden of 0.15 VA, therefor the wiring cannot exceed 0.85VA. The wire you have to extend the CTs is 14 Gauge wire (the mm2 is not an exact conversion). Using the first image the impedance is roughly 0.035 Ohms.

Charles_Murison_0-1752249580057.png


The maximum distance you could extend this wire is very small, way less than 10 feet.

Charles_Murison_1-1752249776311.png

Now if you had METSECT5HA020, the Burden rating of the meter is 1.5VA. Wire maximum burden is 1.35 VA. Impedance is roughly 0.05

Charles_Murison_2-1752249939020.png

 

The maximum distance would be a little less than 10 feet.

Charles_Murison_3-1752250061143.png

To extend the distance between CT and meter the options are to either use thicker wire, or have CT with a larger burden. CTs with larger burden tend to not be as accurate. 

Note that these calculations are to EXTEND the leads of the CT, not replace the leads. The CT's burden ratings already account the the CT leads. How the wire to extend the leads is attached is not a universal answer and different regions have slight different electrical codes so I cannot give a answer specific to your region. You would need to contact an electrician in your area to discuss options.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 6
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-07-08 07:40 AM

0 Likes
4
2334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-08 07:40 AM

Hello @AndersDahlskog ,

If I understand your question, you are wanting to extend the CT lengths by using wire with 2.5mm2 area. Have a look at https://www.se.com/ca/en/faqs/FA221505/ for information.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
AndersDahlskog
AndersDahlskog Contributor
Contributor

Posted: ‎2025-07-10 12:34 AM

0 Likes
3
2310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-10 12:34 AM

Hello @Charles_Murison 

Thanks for your reply, I understand the FAQ. It is a good example and the solution here is to use approx AWG 10 (6mm2) copper cable all the way from CT to meter (shorting block included). What I don`t understand is how to calculate/act to use our H models split core CT´s on page 14 in datasheet  PowerLogic™ Current Transformers (CT) Technical Datasheet | Schneider Electric the cable is a fixed soft cable with approx 16 AWG (1,5mm2) copper cable length approx 2 feet (60cm). There is no secondary screws/lugs for the possibility to use other cable (eg AWG10 as in FAQ example.)

Need some direction/advise how to use/calculate our CT with this model for a correct installation, new file attached.

 

BR/Aders

Attachments
Example of split core CT H models.docx
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-07-10 10:35 AM

0 Likes
2
2302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-10 10:35 AM

Hello @AndersDahlskog .

If I understand your question, you are asking for help to connect The CT leads to a different wire. There are likely local regulations that electrical contractor for your region would know more about. One option could be to use terminal strips and connect CT on one side and larger gauge wires on the other. Perhaps electrician is able to splice cables. Different areas have different regulations so there is unlikely to be a one size fits all solution.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
AndersDahlskog
AndersDahlskog Contributor
Contributor

Posted: ‎2025-07-11 12:00 AM

0 Likes
1
2295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-11 12:00 AM

Hello@Charles_Murison

Thanks for your answer, no my question is: when I have done a calculation a need to use AWG10 (6mm2) cable between CT and meter (like the example in FAQ you mentioned). But Schneider split core CT eg METSECT5HAxxx range has a fixed soft AWG16 (1,5mm2) approx cable attached to it, (see picture in attached file) can´t see that this soft cable can be replaced to calculated need for the installation (in this case AWG10 (6mm2):
How to use this Schneider split core CT eg METSECT5HAxxx range ?, Only limited to use in installations with a calculated need of max AWG16 (1,5mm2) cable between CT and meter ?

Hope this clarify my question and concern

 

BR/Anders

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-07-11 09:27 AM . Last Modified: ‎2025-07-11 09:28 AM

0 Likes
0
2284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-11 09:27 AM

Hello @AndersDahlskog 
Lets assume that you have METSECT5HA025 CT. The maximum burden that this CT can support is 1VA, the Meter has burden of 0.15 VA, therefor the wiring cannot exceed 0.85VA. The wire you have to extend the CTs is 14 Gauge wire (the mm2 is not an exact conversion). Using the first image the impedance is roughly 0.035 Ohms.

Charles_Murison_0-1752249580057.png


The maximum distance you could extend this wire is very small, way less than 10 feet.

Charles_Murison_1-1752249776311.png

Now if you had METSECT5HA020, the Burden rating of the meter is 1.5VA. Wire maximum burden is 1.35 VA. Impedance is roughly 0.05

Charles_Murison_2-1752249939020.png

 

The maximum distance would be a little less than 10 feet.

Charles_Murison_3-1752250061143.png

To extend the distance between CT and meter the options are to either use thicker wire, or have CT with a larger burden. CTs with larger burden tend to not be as accurate. 

Note that these calculations are to EXTEND the leads of the CT, not replace the leads. The CT's burden ratings already account the the CT leads. How the wire to extend the leads is attached is not a universal answer and different regions have slight different electrical codes so I cannot give a answer specific to your region. You would need to contact an electrician in your area to discuss options.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
AndersDahlskog
AndersDahlskog Contributor
Contributor

Posted: ‎2025-07-13 11:54 PM

0 Likes
0
2249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-13 11:54 PM

Hello@ Charles_Murison

A big thank you fore this accurate and good answer

BR/Anders

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore