What would cause reoccurring Time Change Requests on an ION 8560 Meter? The Event Log shows the below Time Change Requests and "Time About to be Changed".
Link copied. Please paste this link to share this article on your social media post.
Hello @Natalie ,
One suggestion would be to look at the clock module settings and if time sync source is set to Ethernet, I suggest you change to the specific protocol you are interested in.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @Natalie
When meter is synchronized(user or software is time sync'ing the meter), the two events 'Time About to be Changed' and 'Time Changed' will be appeared in the Event Log.
If it is not performed by any user, the meter is receiving a time sync packet through the communication line(Ethernet, Serial Com, etc) issued by software that communicates with the meter.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hello @Natalie ,
One suggestion would be to look at the clock module settings and if time sync source is set to Ethernet, I suggest you change to the specific protocol you are interested in.
Regards,
Charles
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.