Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Regarding the unit display of the ION9000 monitor

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Regarding the unit display of the ION9000 monitor
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Miyai
Miyai
Contributor

Posted: ‎2021-12-14 03:14 AM

0 Likes
8
3721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-14 03:14 AM

Regarding the unit display of the ION9000 monitor

Hello,

 

I need advice on the unit notation for Ion9000 monitors.

 

Ia and I4 are written in "kA" notation, while Ib and Ic are written in "A" notation.

I would like to know what the units of "kA" and "A" change based on.

 

Other meters have been pointed out by customers as well, with some units showing "kA" and others showing "A" when the current is less than 100A.

 

The CT settings are as follows.

Primary : 5000A

Secondary : 5A

 

A.png

 

 

Best regards,

Miyai

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-01-19 03:27 PM

0 Likes
1
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-19 03:27 PM

Hello Miyai,

 

I can confirm that like Tomohiro-Okada said, if meter is configured to display kA, either as default setting or display module is set to kA, and the meter measures some current however the display resolution is too small to show, the meter will generate an event and automatically switch units to display A rather than kA. Event text will be something like "Current display value out of range. Reducing scaling)

 

If resolution is 1.x, and the value to display is less than 0.1kA, units will switch to A. If resolution is 1.xx and the display value is less than 0.01kA, units will switch to A.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 8
huseyinb
huseyinb Mentor
Mentor

Posted: ‎2021-12-14 04:00 AM

0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-14 04:00 AM

Hi,

 

firstly install ION SETUP https://www.se.com/ww/en/product-range/61461-ion-setup/

 

connect device with advanced setup parameter and open Display option modules, change default Amper to "A" and send to meter this changed,

 

Br,

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-12-14 10:43 AM

0 Likes
6
3712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-14 10:43 AM

Hello @Miyai ,

 

I moved your question to the metering forum. 
For the ION9000 meter there is concept of Autoscale based on the PT and CT settings. For current, if the CT Primary < 1000, units will default to "A", 1000< CT Primary < 999 999, units will default to "kA" . This can also be overwritten with the display setup register as mentioned already.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Miyai
Miyai
Contributor

Posted: ‎2021-12-14 09:55 PM

0 Likes
5
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-14 09:55 PM

Hello @Charles_Murison , @huseyinb 

 

Thank you for advise.

I have checked the Ion setup and I have two questions.

 

(1) When ”Display option modules” was changed, the 3 phases (Ia, Ib and Ic) were changed all together.

   However, in this case, Ia is "kA" and Ib and Ic are "A". Do you know why this is? Could it be a glitch?

kA.png

 

(2) Is the meter's factory default setting for Display option modules set to "Default"?

 The customer who set up this meter is changing the settings on the monitor.

  Therefore, customers are not using Ion setup.

 

 

Best regards,

Miyai

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-12-15 11:16 AM

0 Likes
4
3690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-15 11:16 AM

Hello @Miyai ,

 

I will say I have not seen that before but recommend working with technical support (se.com ->support ->contact support) for troubleshooting. Would be good to know what is getting feed into the data mapping module (see modus map document). In ION Setup if you hold down shift and click on inputs tab you will see a snapshot of the real time values.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Miyai
Miyai
Contributor

Posted: ‎2021-12-15 04:14 PM

0 Likes
2
3682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-15 04:14 PM

Hello @Charles_Murison 

 

Thank you for advise.

I'll try contacting tech support.

 

However, it is difficult to connect with ION setup as I have already left the meter.

 

 

Best regards,

Miyai

Tags (1)
  • Tags:
  • english
Reply
T.Okada
T.Okada
Contributor

Posted: ‎2021-12-20 12:36 AM

0 Likes
0
3668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-20 12:36 AM

Hi Charles,

 

I did some verification on this with ION9000 meter.

(CT setting  is 5000:1000A, Current Resolution setting is 1.XXX)

 

At first the display unit of current is "kA" as you said, because CT primary setting is over 1000A.

Then, I applied 0.200A current by using current generator (It means the meter displays 0.001kA.)

and ION9000 meter displays "0.001kA" correctly.

 

Next, I reduced the current input gradually and the display unit turns from "kA" to "A".

 

After that I did further testing and found the following.

 

When the input current to the meter is 0.000A on the primary side,

the display unit of current is "kA".

 

When the input current to the meter is 0.001-0.999A on the primary side,

the display unit of current turns from "kA" to "A".

 

When the input current to the meter is over 1.000A on the primary side,

the display unit of current is "kA".

 

I think it is for preventing from electric shock.

(In this case, if input current of primary side is 0.100A and the meter keeps displaying current by using "kA",

 user of the meter misunderstand there is no current on the circuit.)

 

Is my understanding correct?

 

Regards,

Okada

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-01-19 03:27 PM

0 Likes
1
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-19 03:27 PM

Hello Miyai,

 

I can confirm that like Tomohiro-Okada said, if meter is configured to display kA, either as default setting or display module is set to kA, and the meter measures some current however the display resolution is too small to show, the meter will generate an event and automatically switch units to display A rather than kA. Event text will be something like "Current display value out of range. Reducing scaling)

 

If resolution is 1.x, and the value to display is less than 0.1kA, units will switch to A. If resolution is 1.xx and the display value is less than 0.01kA, units will switch to A.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Miyai
Miyai
Contributor

Posted: ‎2022-02-08 09:26 PM

0 Likes
0
3516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-08 09:26 PM

Hello @Charles_Murison 

 

Sorry for late reply.

 

At the end of last year, I verified with ION9000 and verified the same content as your advise.

It has already been answered to the customer.

 

Thank you for your support.

 

Best regards,

Miyai

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore