Hello @arjan_greenwave @arjan_greenwave @sesa102217_brid
Wanted to let you know the latest release of firmware is available to address the modbus N/A exception.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi - what are the communication settings on the PM8000? Has the protocol been changed from ION to Modbus for the communications port you are using?
Thanks
Tom
Link copied. Please paste this link to share this article on your social media post.
I´m using modbus TCP for Comx210 communication with PM8000.
attached some screens.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
There is a Modbus TCP security setting shown in the attached picture - worth ensuring it is on. Does the ComX indicate whether the connection is successful, but cannot read, or is the connection not succeeding? (There is a setting in the Security Options module to disable read access for Modbus).
Tom
Link copied. Please paste this link to share this article on your social media post.
I have other meters (iem and pm5560) modbus and modbus TCP already working on this comx210.
Only the PM8000 that was installed now doesn't work,
and checking in IONsetup the modbus tcp connection is active.
Tks
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa102217_brid ,
Are you able to read the modbus registers using a modbus client like in FA180037 . This would help determine if there could be something on the PM8000 or the gateway to investigate further. While connected to the meter in ION Setup. Switch to advanced configuration -> Security Option Modules -> Security Option module 1 -> Setup registers -> Modbus Map access, Be sure that read or read/write is selected.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi, Charles.
Yes,
I can read modbus logs through another client, I used modscan.
Regarding the advanced option, it was read-only and I changed it to read and write, but still no communication.
On the 3rd party protocols Communication screen the default modbus slave is showing N/A.
Do you know if it's normal?
Tks
Link copied. Please paste this link to share this article on your social media post.
In another test I did, I changed the driver from pm8000 to PM5560 and the readings started to appear,
wrong but communicated.
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa102217_brid ,
Having the default Modbus Slave showing "Default" as N/A is normal when there are no custom modbus registers. The PM8000 meters support 3 different configurations, Default only, Default + custom, Custom only.
I do not have a Com'X so I am not 100% sure of the driver. I am wondering if possible that a request to the meter includes registers that are "N/A" inside the meter. For example power factor leading if you have a lag system. If this is the case, 3 options,
1) Wait for the next release of meter firmware (currently under development)
2) If registers in the request are known to always be N/A, it is possible to unlink the registers from the data mapping module in question
3) Place a convert module in front of the data mapping module to convert N/A to either 0 or 1 depending on the need.
4) I am not sure if this is possible, modify the PM8000 driver to not include the N/A registers. Without knowing exactly what the driver is requesting I can't give more specifics. If the driver is doing big block reads, perhaps change to multiple smaller block reads. If already small block reads, either modify blocks to be smaller to avoid the N/A or remove the block completely if not needed.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
hi,
I have the same problem
Seems that the PM8000 Modbus driver is not working.
When I select PM5560 data is coming through.
Seems like this wasn't resolved?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hi, Arjan.
Not yet, but I created a custom driver for pm8000 on comx210,
if you need me let me know that I'll forward it to you.
Send e-mail for me.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @arjan_greenwave ,
I have the same behavior on my Com'X510 v6.8.4:
Issue is related to the current FW Version 3.0.0 of the PM8000 / ION9000 platform. Things will not change until next release of PM8000 FW release (no date confirmed yet). This is not planned to update the ION native models to change the Modbus Registers polling method.
You can try to apply the workaround provided by Charles above or in the following thread:
Or also create a custom PM8000 driver mapping the register you want to log and publish.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @arjan_greenwave @arjan_greenwave @sesa102217_brid
Wanted to let you know the latest release of firmware is available to address the modbus N/A exception.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Charles_Murison ,
It seems that the upgrade to v3.1.0 do not fix the issue with the Com'X.
Update on the following thread:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello Romain,
Randi was able to test with a Com'X and did not have trouble connecting to PM8000 and reading values.
Regards,
Charles