Comx210 reading PM8000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Comx210 reading PM8000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa102217_brid
Ensign sesa102217_brid Ensign
Ensign

Posted: ‎2021-08-05 07:59 AM

0 Likes
18
10342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-05 07:59 AM

Comx210 reading PM8000

I have a problem, with Comx210 it is not reading PM8000 meter, but if I select another driver like pm5000 I can read it.
Comx210 is with the latest firmware v6.8.4 and PM8000 v3.0.0
thanks in advance.

Labels
  • Labels:
  • ION8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa102217_brid
Ensign sesa102217_brid Ensign
Ensign

Posted: ‎2021-08-11 04:53 AM

0 Likes
0
10250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-11 04:53 AM

 @Charles_Murison  the customer will wait for the next release of meter firmware.

 

Thanks

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-11-16 08:19 AM . Last Modified: ‎2022-10-19 01:16 AM

0 Likes
2
7666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-16 08:19 AM

Hello @arjan_greenwave  @arjan_greenwave  @sesa102217_brid 

 

Wanted to let you know the latest release of firmware is available to address the modbus N/A exception.

 

https://community.se.com/t5/Metering-Power-Quality/New-Firmware-version-3-1-0-for-Advanced-Meters-is...

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 18
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2021-08-05 08:56 AM

0 Likes
17
10334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-05 08:56 AM

Hi - what are the communication settings on the PM8000?  Has the protocol been changed from ION to Modbus for the communications port you are using?

 

Thanks


Tom

Tags (1)
  • Tags:
  • english
Reply
sesa102217_brid
Ensign sesa102217_brid Ensign
Ensign

Posted: ‎2021-08-05 10:48 AM

0 Likes
2
10329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-05 10:48 AM

I´m using modbus TCP for Comx210 communication with PM8000.
 attached some screens.
Attachments
Tags (1)
  • Tags:
  • english
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2021-08-05 11:14 AM

0 Likes
1
10323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-05 11:14 AM

Are  you able to connect to the device with ION Setup?

Tags (1)
  • Tags:
  • english
Reply
sesa102217_brid
Ensign sesa102217_brid Ensign
Ensign

Posted: ‎2021-08-05 11:17 AM

0 Likes
0
10321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-05 11:17 AM

Yes, 

Tags (1)
  • Tags:
  • english
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2021-08-05 12:09 PM

0 Likes
13
10319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-05 12:09 PM

There is a Modbus TCP security setting shown in the attached picture - worth ensuring it is on.  Does the ComX indicate whether the connection is successful, but cannot read, or is the connection not succeeding? (There is a setting in the Security Options module to disable read access for Modbus).

 

Tom

Attachments
Tags (1)
  • Tags:
  • english
Reply
sesa102217_brid
Ensign sesa102217_brid Ensign
Ensign

Posted: ‎2021-08-05 12:40 PM

0 Likes
12
10315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-05 12:40 PM

 

I have other meters (iem and pm5560) modbus and modbus TCP already working on this comx210. 
Only the PM8000 that was installed now doesn't work, and checking in IONsetup the modbus tcp connection is active.

Tks

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-08-05 01:15 PM

0 Likes
11
10313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-05 01:15 PM

Hello @sesa102217_brid ,

 

Are you able to read the modbus registers using a modbus client like in FA180037 . This would help determine if there could be something on the PM8000 or the gateway to investigate further. While connected to the meter in ION Setup. Switch to advanced configuration -> Security Option Modules -> Security Option module 1 -> Setup registers -> Modbus Map access, Be sure that read or read/write is selected.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
sesa102217_brid
Ensign sesa102217_brid Ensign
Ensign

Posted: ‎2021-08-06 06:39 AM

0 Likes
10
10299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-06 06:39 AM

Hi, Charles. 

 

Yes, 

I can read modbus logs through another client, I used modscan.
Regarding the advanced option, it was read-only and I changed it to read and write, but still no communication.
On the 3rd party protocols Communication screen the default modbus slave is showing N/A.
Do you know if it's normal?

Tks 

Attachments
Tags (1)
  • Tags:
  • english
Reply
sesa102217_brid
Ensign sesa102217_brid Ensign
Ensign

Posted: ‎2021-08-06 06:43 AM

0 Likes
7
10298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-06 06:43 AM

In another test I did, I changed the driver from pm8000 to PM5560 and the readings started to appear, 
wrong but communicated.

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-08-06 09:01 AM

0 Likes
1
10291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-06 09:01 AM

Hello @sesa102217_brid ,

 

Having the default Modbus Slave showing "Default" as N/A is normal when there are no custom modbus registers. The PM8000 meters support 3 different configurations, Default only, Default + custom, Custom only. 

 

I do not have a Com'X so I am not 100% sure of the driver. I am wondering if possible that a request to the meter includes registers that are "N/A" inside the meter. For example power factor leading if you have a lag system. If this is the case, 3 options,

 

1) Wait for the next release of meter firmware (currently under development)

2) If registers in the request are known to always be N/A, it is possible to unlink the registers from the data mapping module in question

3) Place a convert module in front of the data mapping module to convert N/A to either 0 or 1 depending on the need.

4) I am not sure if this is possible, modify the PM8000 driver to not include the N/A registers. Without knowing exactly what the driver is requesting I can't give more specifics. If the driver is doing big block reads, perhaps change to multiple smaller block reads. If already small block reads, either modify blocks to be smaller to avoid the N/A or remove the block completely if not needed.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
sesa102217_brid
Ensign sesa102217_brid Ensign
Ensign

Posted: ‎2021-08-11 04:53 AM

0 Likes
0
10251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-11 04:53 AM

 @Charles_Murison  the customer will wait for the next release of meter firmware.

 

Thanks

Tags (1)
  • Tags:
  • english
Reply
arjan_greenwave
Lieutenant | EcoXpert Master arjan_greenwave Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2021-09-27 06:12 AM

0 Likes
6
9033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-27 06:12 AM

hi,

I have the same problem

 

Seems that the PM8000 Modbus driver is not working.

 

When I select PM5560 data is coming through.

 

Seems like this wasn't resolved?

 

 

Regards,

 

Tags (1)
  • Tags:
  • english
Reply
sesa102217_brid
Ensign sesa102217_brid Ensign
Ensign

Posted: ‎2021-09-27 06:22 AM

0 Likes
1
9030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-27 06:22 AM



Hi, Arjan.

 

Not yet, but I created a custom driver for pm8000 on comx210,

 

if you need me let me know that I'll forward it to you.

 

Send e-mail for me. 

Tags (1)
  • Tags:
  • english
Reply
arjan_greenwave
Lieutenant | EcoXpert Master arjan_greenwave Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2021-09-27 06:31 AM

0 Likes
0
9027
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-27 06:31 AM

arjan@greenwave.co.za

 

Thank you will appreciate it!

 

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2021-09-27 06:32 AM . Last Modified: ‎2022-10-19 01:24 AM

0 Likes
3
9026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-27 06:32 AM

Hello @arjan_greenwave , 

I have the same behavior on my Com'X510 v6.8.4:

  • PM8000 v2.1.0 is working fine with the native Com'X model
  • ION9000 v3.0.0 is not working as expected with the native model

 

Issue is related to the current FW Version 3.0.0 of the PM8000 / ION9000 platform. Things will not change until next release of PM8000 FW release (no date confirmed yet). This is not planned to update the ION native models to change the Modbus Registers polling method.

 

You can try to apply the workaround provided by Charles above or in the following thread:

https://community.se.com/t5/Metering-Power-Quality/The-Value-of-quot-N-A-quot-register-of-PM8000-fir...

Or also create a custom PM8000 driver mapping the register you want to log and publish.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-11-16 08:19 AM . Last Modified: ‎2022-10-19 01:16 AM

0 Likes
2
7667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-16 08:19 AM

Hello @arjan_greenwave  @arjan_greenwave  @sesa102217_brid 

 

Wanted to let you know the latest release of firmware is available to address the modbus N/A exception.

 

https://community.se.com/t5/Metering-Power-Quality/New-Firmware-version-3-1-0-for-Advanced-Meters-is...

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2022-02-09 01:53 AM . Last Modified: ‎2022-10-19 01:07 AM

0 Likes
1
5752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-09 01:53 AM

Hello @Charles_Murison , 

 

It seems that the upgrade to v3.1.0 do not fix the issue with the Com'X.

 

Update on the following thread:

https://community.se.com/t5/Gateways-and-Energy-Servers/PM8000-predefined-model-for-COMX210-fw-6-8-4...

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-02-09 08:29 AM

0 Likes
0
5740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-09 08:29 AM

Hello Romain,

 

Randi was able to test with a Com'X and did not have trouble connecting to PM8000 and reading values.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of