Hi
I would like to use the logging function of HDPM6000 with PME.
I tried it myself, and while the branch circuit logging is working, the main feeder logging sometimes does not, so the behavior feels unstable. Please tell me the settings required to make logging work properly on PME with the HDPM6000. Do I also need to configure logging in the HDPM browser screen? If I want to log the currents for both the main feeder and the branch circuits, what is the appropriate way to configure the settings?
Regards,
Okada
Link copied. Please paste this link to share this article on your social media post.
Hi @T.Okada
In the following HDPM6000 forum, you will find a sample configuration file that sets up the head unit onboard logs to match the configuration expected by the PME HDPM6000 driver.
HDPM6000 Sample Configuration Files
After uploading the file HDPM6000-v0.62.7-PME-logging-v1.cfg to the HDPM6000 meter, I was able to view the logged values in PME for both the PQM and the branch circuits. You can verify the new settings in the Logging tab for each parameter.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @T.Okada
In the following HDPM6000 forum, you will find a sample configuration file that sets up the head unit onboard logs to match the configuration expected by the PME HDPM6000 driver.
HDPM6000 Sample Configuration Files
After uploading the file HDPM6000-v0.62.7-PME-logging-v1.cfg to the HDPM6000 meter, I was able to view the logged values in PME for both the PQM and the branch circuits. You can verify the new settings in the Logging tab for each parameter.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @Mehran_Mehrnia,
Thank you for your reply.
I downloaded the configuration files you mentioned and they work well.
Regards,
Okada